I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N & E. Typically they plug into a holder, sometimes as two separate SPDs (e.g. Hager, with separate E connections), more often now as one combined SPD (e.g. Fusebox) with one each of L, N & E connections.

For a TN-C-S supply where N & E are typically connected a very short distance way (e.g. well under 3m), can someone tell me why the SPD across N & E is actually needed?

I can see the merit for TT and maybe TN-S supplies, and wonder is it just to simplify making only one devices that will serve all applications?

Do single module Type 2 SPDs for use across just L & E actually exist?
 
  • Like
Reactions: Pretty Mouth
Good question. At a guess, I'd say the voltage drop between the SPD and the N-E connection at the cutout could be significant. So there could be a potential difference between N and E within the installation.
 
  • Like
Reactions: pc1966
Do single module Type 2 SPDs for use across just L & E actually exist?
Yes, for example:

However, the reality is the L-N-E style are far more useful in general as they can be used for all style of earthing (as the risk of L shorting via N to E is negligible for TT use) and it reduces the need to worry about the inductance of the cabling from, for example, the N-E joint in a TN-C-S system to the point where the SPD is fitted.

As you need to keep the inductance down for the very high dI/dt of a lightning surge, and so total loop distance from L via SPD to N/E to no more than 1m and ideally less than 0.5m, you can only usefully deploy a single module SPD if the cutout is very close to the CU or similar where the SPD is fitted.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

SJD

Mentor
Arms
~
Joined
Location
Braccan heal
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
Running own small electrical company.

Thread Information

Title
Surge protection devices for PME supplies?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
SJD,
Last reply from
pc1966,
Replies
2
Views
1,174

Advert