Search the forum,

Discuss 2391 written exam last nite in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

There seems to be a unanimous conclusion that these 2391 exams aren't worded very well. How many folks took this exam on here? I'm thinkin we should start a revoloution or something, at the least get a petition sent out to ****** and no thrills telling them that whoever writes out this exam wants sacking!!!
 
Last edited by a moderator:
I doubled the length of the conductors, but now I'm confused:

Table 4D1B in Appendix 4 states that 10mm sq cable in conduit drops 4.4mV/A/m at 70 °C
The title at the top states: 'Single-core ... cables', so I'd assume the values are for one conductor only.

The table in the question paper is different. 'Figure 1 below shows information on the resistance of conductors in mΩ/A/m.'
The bottom row says nothing more than: 1m of a 10mm² conductor has a resistance of 1.83mΩ at 20°C.
At 1amp, this gives a voltage drop of 1.83mV.
The scenario also mentions single cables in trunking and conduit.

Sadly, when I compare the figures with BS7671, logic and common-sense cease to apply.
The values on the exam paper should be the same as the values listed in BS7671, table 4D1B, but reduced a certain amount because they're at 20°C instead of 70.

BS7671 says a 1m length of 10mm ² cable drops 4.4V per amp,
C&G say that the same cable drops 1.83mV.

Temperature correction is 4% increase in resistance per 10°Cincrease in temperature, i.e. 20% for a 50°C difference.


The difference in these two figures is 58%.

What's going on?

The 4.4 mV/A/m is for 2 cables (L+N) single phase 10mm copper conductor at 70 degrees.
if you divide that by 2 you get 2.2 mV/A/m for one 10mm conductor at 70 degrees

The mV/A/m value is doubled to add the neutral conductor so you dont need to double the length. Just use the length of the run.

The 1.83mΩ/m is at 20 degrees.
Temperature correction is 4% increase in resistance per 10°Cincrease in temperature, i.e. 20% for a 50°C difference.

so 1.83 x 1.2 (20%) = 2.2mΩ/m (at 70 degrees)

mV/A/m is the same as mΩ/m
 

Reply to 2391 written exam last nite in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock