Discuss 30 amp rewireable fuse + 1.0mm cpc in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Des 56

-
Esteemed
Arms
Reaction score
6,093
Having been one of the culprits who wired 2.5 ring mains with 1.0mm cpc in times past
I am going to do some repositioning of sockets in a kitchen which is being extended
It has rewireable fuses pre-dating the standard wylex rewireables

Before taking on the work I tested the existing ring and looked in the good book for max zs because there is no chance whatsoever of rewiring for various reasons
Having in the past seen and used 30 amp fuses for these on numerous occasions,I was surprised they appear to be not listed in the on site guide
The way I am reading it,30 amp fuses on a 1.0mm cpc ring are not permitted
(Having said that working my way through guide books has never been a strong point with me)

Is this correct or am I cocking up somewhere?
The only reason I can come up with is possible thermal effects on the 1.0mm cpc

Your advise and/or knowlege would be greatly appreciated
 
Des 3o fuses and 32a mcb,bs88 (with rcd protection) is ok.

With rings it is esentially a duel supply to each point so its 5mm and 2mm cpc.
As its a ring what is assumend on a perfect situation is 16a load per leg to md pot so your "2.5d 1mm cpc is allowed. If in dought try the adiobatic to prove ring size section its arround section 520530 of BRB
 
Table 41.2 of the brg, max Zs for a 30 amp fuse to BS 3036 1.09 ohms.
Appendix 15 conductor size of ring, live=2.5mm, cpc=1.5mm

However, 433.1.3 say where the protective device is BS3036, you must de-rate the current carrying capacity of the cable by 0.727.

So, add this to the need for rcd protection, you should change the protective device to an rcbo or better still fit a new consummer unit.

As to wether you can extend a final ring circuit that has a 1mm cpc rather than rewire the whole circuit.................

I dont know!
 
Thanks for the reply scotsparky
I have done the adiabatic and its ok
What was throwing me was the statement at the bottom
The combination of the protective conductor and the fuse is not permitted


If I assume equal load down both legs and 2x1.0mm cpc then the statement does not apply?

Table 41.2 of the brg, max Zs for a 30 amp fuse to BS 3036 1.09 ohms.
Appendix 15 conductor size of ring, live=2.5mm, cpc=1.5mm

However, 433.1.3 say where the protective device is BS3036, you must de-rate the current carrying capacity of the cable by 0.727.

So, add this to the need for rcd protection, you should change the protective device to an rcbo or better still fit a new consummer unit.

As to wether you can extend a final ring circuit that has a 1mm cpc rather than rewire the whole circuit.................

I dont know!


There is an existing 30 m/amp rcd and the main earth conductor and protective bonding are to standard
The lenghth of circuit will not be extended as such
I have suggested a new consumer unit,but the soon to be kitchen fitter has already agreed with the householder to fit one later on(thats one reason why I am checking the compliance before commencing the work, I may have reason to quote for the consumer unit before him (defined scope or not he is taking work off me,maybe work he should not be doing )
I will be working for a builder and will do whats required for him,but my install/alteration needs to be correct ,new consumer or not,but the guide threw a panner at my understanding
Thanks for the replies
 
Last edited:

Reply to 30 amp rewireable fuse + 1.0mm cpc in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Carrying out and EICR on large factory and they have welding plug into 63 amp commando sockets but are protected by 30 amp BS 88 fuses. Now...
Replies
11
Views
7K
Hi everyone. I'm an electrician in Leeds and i'd really appreciate your view on walking away from jobs when the existing install is not right...
Replies
36
Views
5K
Hi all. Thank you all in advance for your help and advice. I was hoping to get some help and advice on a cooker issue I'm experiencing. My...
Replies
91
Views
10K
T
Hi, First let me just say that I am not an electrician although in the past I've done the usual garage and shed wiring without having any...
Replies
24
Views
8K
Thai Amateur
T
S
Hi folks, Newbie here. Many thanks in advance for an suggestions or help given. I am wondering about getting a new consumer unit fitted in my 3...
Replies
24
Views
4K
Spudnik
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock