Testing today. Zs produced an Err 4 reading on the Fluke MFT, so I got the wander lead out and connected to the MET. No continuity but 60 (ish) volts difference showing on the display.
Any ideas?
Any ideas?
Happy hunting!It's actually a minor works. Intending to extend lighting circuit from that point.
Looks like I'll be spending my Saturday looking for a missing CPC. Oh joy.
It's actually a minor works. Intending to extend lighting circuit from that point.
Looks like I'll be spending my Saturday looking for a missing CPC. Oh joy.
My top tip for you .... Doing a Zs at the point you wish to extend from .... And make 100% sure any pricing you give allows for unexpected issues arising and you can charge the client more ...
A very conveniently round mft Figure .(on a secondary display ?).....the 60V.
A very conveniently round mft Figure .(on a secondary display ?)
Warning of danger rather than acuracy !
( High input resistance of mft lets it get that high )
- would be lower if you put your finger there -
( not a suggestion ! )