Testing today. Zs produced an Err 4 reading on the Fluke MFT, so I got the wander lead out and connected to the MET. No continuity but 60 (ish) volts difference showing on the display.

Any ideas?
 
Sounds like there’s no earth continuity on the circuit. Was the circuit live when you tested with wander lead? The 60v is likely to be an induced or floating voltage on the unearthed conductor.
 
There’s no earth at that point in the circuit plus something has caused a potential of 60 volts to earth to appear on the earth terminal at that point.
I assume this is an EICR since you have carried out the efli test before the continuity of cpc so you need to code it accordingly.
 
It's actually a minor works. Intending to extend lighting circuit from that point.

Looks like I'll be spending my Saturday looking for a missing CPC. Oh joy.
 
It's actually a minor works. Intending to extend lighting circuit from that point.

Looks like I'll be spending my Saturday looking for a missing CPC. Oh joy.

My top tip for you .... Doing a Zs at the point you wish to extend from .... And make 100% sure any pricing you give allows for unexpected issues arising and you can charge the client more ...
 
My top tip for you .... Doing a Zs at the point you wish to extend from .... And make 100% sure any pricing you give allows for unexpected issues arising and you can charge the client more ...

It's a longstanding client luckily so it's all day rate.

Found the issue, broken CPC in a pendant, possibly moved by a decorator. (Not that I'm pointing fingers).

It wasn't the lack of earth continuity that puzzled me so much as the 60V.
 
with a broken cpc , it's common to read a voltage on the part of the cpc that is not connected. commonly known as a floating voltage. could be induced from current carrying cables in close proximity. once the cpc has been repaired, that voltage will be like Donald Trump's personality. totally disappeared.
 
A very conveniently round mft Figure .(on a secondary display ?)
Warning of danger rather than acuracy !
( High input resistance of mft lets it get that high )
- would be lower if you put your finger there -
( not a suggestion ! )

Never should have moved from needles to LCD...
Although,of course,this may have dulled the enjoyment,of an Xbox:)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
South East
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
60 volts on an R2 long lead test?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
10

Thread Tags

Advert

Thread statistics

Created
South Spark,
Last reply from
PEG,
Replies
10
Views
2,840

Advert

Back
Top