I’m not sure any DNO have any reservations on exporting/extending pme supplies in a domestic installation.

What Scheme are you with?
niceic
IF the outbuilding has NO exposed conductive parts & thus no introduced low resistance earth path then the PME can be exported.
e.g. total wooden shed on support battens with no pipework entering the shed...
This will meet BOTH of the above regs so OK exported.
Obviously if the house supply was TT or TNS the max fault current down the earth conductor would NEVER be the full load current. e.g. a broken neutral in these situations would just mean NO power!https://talk.electriciansforums.co.uk/uploads/emoticons/default_plain.gif
so only a smaller CSA earth needed to safely export earth.

which is why i said check not a must do.
 
western power is my area and ive been shoulder tapped by my governing body before on a visit
tt allows for higher than 35ohms at db
Hi drilltoaster, I've had a good look into the whole 'DNO forbids exporting PME earth' thing, and it would appear to be a myth. I can find no evidence that any DNO outright forbids it, and neither can anyone else when challenged.

For western power, the best information I can find comes from their website, click on 'Can you provide an earthing terminal'


In short, if everything meets BS7671 and Engineering Recommendation G12 then you're good to go.

 
Can someone explain to me what this phrase "exporting PME" actually means, and if it is actually mentioned in bs7671?

I think it strictly means selling PME to another country, which is utter nonsense.

It is a phrase used incorrectly, usually by people who get their knowledge from rumours and what their mates tell them in the pub, to refer to extending the equipotential zone of a PME installation to outbuildings.
[automerge]1578169573[/automerge]
western power is my area and ive been shoulder tapped by my governing body before on a visit
tt allows for higher than 35ohms at db

A governing body tapped you on the shoulder???

Do you mean the assessor from a competent person scheme talked to you about this and you believed everything they told you without checking the facts and theory for yourself?
 
Hi drilltoaster, I've had a good look into the whole 'DNO forbids exporting PME earth' thing, and it would appear to be a myth. I can find no evidence that any DNO outright forbids it, and neither can anyone else when challenged.

For western power, the best information I can find comes from their website, click on 'Can you provide an earthing terminal'


In short, if everything meets BS7671 and Engineering Recommendation G12 then you're good to go.


i never said forbid
i got a dilemma for you
2 core swa installed in ground by house builder (major builder) already supplying a db in garage ze is 175 ohms what do you do?
scenario
customer wants a new consumer unit installed in the detached garage.
main incomer to building is on other side of house approximately 20 mtrs away new cable route if required is via grass and concrete, clay and rock is located in ground approximately 18inches if lucky.
 
i never said forbid
i got a dilemma for you
2 core swa installed in ground by house builder (major builder) already supplying a db in garage ze is 175 ohms what do you do?
scenario
customer wants a new consumer unit installed in the detached garage.
main incomer to building is on other side of house approximately 20 mtrs away new cable route if required is via grass and concrete, clay and rock is located in ground approximately 18inches if lucky.
i forgot to mention current ze is armour cpc
 

Reply to Advice needed for garage power job in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
903
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock