Discuss Advice needed for garage power job in the UK Electrical Forum area at ElectriciansForums.net
No one is trying to roast you. If you have a Ze of 0.22 and a Zs of 175 in the garage this points to a breakdown of earth continuity, the armour is almost certainly not effectively earthed.
Westward, swa armouring is the most obvious place to start looking, but would/could you see similar figures with an issue on the line side of the loop? Loose/poorly made terminations for example?
Yes a fault in the line could cause this, but then everything it supplies would have stopped working, or at least not work properly.
And installing an earth rod certainly wouldn't disguise the problem
Reply to Advice needed for garage power job in the UK Electrical Forum area at ElectriciansForums.net
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
4K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
  • Locked
5K
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...