I'm at a large factory and they are complaining that all the lights flicker now and then. I've tested between earth and n at the intake and the voltage is fluctuating between 20 50 volts which isn't that bad but we are going to check all n connections where we can. Could be a supply problem?
 
what's the L/N and L/E voltage readings?
 
The figures don’t make sense 235V L/N L/E, but fluctuating 20/50V N/E.
Get the DNO in pronto.

Out of interest is this a three phase supply?
 
I’m concerned that for a start you think 50V N/E is quite acceptable.
L/E may stay stable, but L/N must be fluctuating.
 
You say this is a large factory, .....Got any ''Large Motors'' starting and stopping?? also is there any facility of Static or Auto capacitor banks at the main intake?? Both can cause problems with voltage fluctuations, the latter when not set-up properly....
 
Good question E54.

Please let us know the answer King_11.
PS exactly what I suspected, but you were evasive in giving an answer.
 
I'm thinking ....Large Factory, = Electrical Supply from 11KV via DNO or factory owned transformer(s). Very unlikely the DNO will provide a LV 400/230V to a large factory... lol!!! Cheaper unit charges too, when being supplied at MV tension. ..lol!!
 
No probs King. Wasn't meaning any disrespect to you, just that it seems to happen alot, someone posts an issue, and we never hear back to see how or what was done to rectify their problem
 
lucky they found that neutral - could have been a mess if it got hot - iv seen some big 600A supplys melted at the terminals :S
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
all lights in building intermittently flickering
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
king_11,
Last reply from
shocking_eg,
Replies
14
Views
1,950

Advert

Back
Top