I

iwantmyNVQ

Hi guys i calculating my expected maximum demand for an installation to see if the 60A cut out will handle it.

heres what will go in and calculations incl diversity

2X 32A Rings, so 32A(first ring) + 12.8A (40% all others)
1X 6A lighting, so 4A (66%)
1X10A lighting, so 7A
1X32A Shower, so 32A
1X45A cooker, 10A+ 40%of 35A= 24A
1X32A Under floor heating, 32A

so this equals 144A????

am i missing something this isnt right!!
 
Ive always taken the biggest mcb away, then add the others togehter, then divide them by 4, then add back the biggest one. Which is about 81A but I doubt you will get anywere near this as it is unlikly you will have everything on all at once.



Jay
 
Last edited:
so if i do that it comes to 81A, but ive only got a 60A cut out! what can i do client wants to do away with gas heating and oven so everythings going electric!
 
Its very unlikley you will have everything on all at once. So IMO the 60A should be ok. But if hes adding more stuff then this will need recalculating and maybe then the cut out will need upgrading.

Jay
 
thanks for the advice jay, its in a block of flats and the suppliers armoured looks about 10mm so is upgrading the cut out an option, surely 80/100 A would require a 25mm, considering its a good 80M run.....

no its a TNS morph...

i understand scientifically that load wont be reached but what happens when it comes to writing out the certs and my demand is higher than the cut out>?:crazy:
 
When I first started doing testing for a company a few years ago, I asked what should I put in the max demand if it calculated over the cut out rating and they said put half the cut out rating. But now, if its more I just put the acctual size of the cut out because in theory the installation cant demand more that the cut out anyway. A standard 2/3 bedroom house will pull roughly 45A max.

Jay
 
hi
if tns you could get a 100 A put in , however i would just jot done 60A as max demand they wont say owt, its all a bit finger in the air really anyway to be honest
i have all leccy and a 6o A main fuse and all is cool
 
yeah that makes sense obv the max USED demand cant be higher than the cut out as itl blow but from the assesors point of view he will notice my design current is higher than my supply will allow so im worried about being pulled up on it. would an explanation that even though there are two rings for functionality of the computer room niether of the rings will be pulling anywhere near 10A!!

thanks jay this is reassuring and well needed meeting with the client tomorrow to tell them if we can go electric UFH or wether we will have to go for a wet system
 
I was pulled up on my NIC inspection for putting 60 Amps, i said yes i know with gas central heating, no shower and gas hob it probably should be near 40 Amps.

No he replied, because i had put in a lot of circuits he worked it out for me. The answer 160 Amps!!!!!

I just tell them the method i use to work it out now is common sense! Doesn't always go down well though.
 
I think the underfloor heating should be ok. I dont think your assessor will have a problem with it. To be on the safe side you coud ring the DNO and tell them what circuits you have and what circuits you will be adding and see what they say. But if they need to upgrade the main cut out it may cost you loads.

Good luck with the assessment

Jay

As TC says, the assesor could be a burke.
 
Last edited:
I was pulled up on my NIC inspection for putting 60 Amps, i said yes i know with gas central heating, no shower and gas hob it probably should be near 40 Amps.

No he replied, because i had put in a lot of circuits he worked it out for me. The answer 160 Amps!!!!!

I just tell them the method i use to work it out now is common sense! Doesn't always go down well though.


so he was telling you to put 160A thats ridiculous!!
 
pahaha sounds about right!!

so can i take the understanding that even tho through applying diversity and the relevant calculations my design current can be higher than the cut out as the likelyhood of it reaching that load is slim?
 
pahaha sounds about right!!

so can i take the understanding that even tho through applying diversity and the relevant calculations my design current can be higher than the cut out as the likelyhood of it reaching that load is slim?

technically no because design current is what you will really draw,
diversity is different in real terms , also i think its 30 % of full load not 40 % as you mentioned earlier
just put 60 A i would be amazed if the assessor says anything, dont stress it out
 

Reply to Am i wrongly calculating my maximum demand? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock