I assumed it’s a typo.why minimum and not maximum
The way I read the question is you would select the cable on the size of protective device so it would have a bearing on it. Ib<In<IzType of protective device would have no bearing on the CCC of a cable.
So with a 20A radial, what effect would the 20A protective device have on the CCC of the cable used to wire the circuit?The way I read the question is you would select the cable on the size of protective device so it would have a bearing on it. Ib<In<Iz
Surly if a protective device is C then the CCC of cable has to be above C but as for the minimum, it could be anything you want just so long as the protective device will trip before the maximum is reached.You take a protective device of current rating C, the minimum current carrying capacity of a live conductor connected to this protective device is C
Yes, on a sober mind this morning it all becomes clear. I completely agree.The current carrying capacity of the cable must be greater than or equal to C, e.g. if C is 10 then CCC could be 10, 20, 540, 2340. However the minimum value is 10. It cannot be lower than this.