good morning all.

Im getting sick of working for other people, so ive decided that im gona register with a scam, and then see if i can get enough work to jack in agency stuff.

For my assesment, i intend to split tails at main head, switchfuse or 4way board with isolator and 32Amcb supplying 6mm2 swa to garage. in garage 6way board for power, lighting, future garden lighting and 110v tranny spurred off power. sockets all RCD sockets, apart from one which i want for testing RCDs ect. everything in PVC tube.

house is TNC-s

as per the title, the garage is attached, but do the requiremnts still apply for outbuildings? there is not internal access to garage from house. also ive ive got one bit of maybe extraneous (not tested yet) metalwork in the garage, but it is a tiny bit of copper pipe supplying a tap, and its half buried in a wall.
if the garage is classed as an outbuilding, then according to the brb i have to run 10mmg/y to the garage. the thing is, the house CU is only 6m away, and IMO the ground potential will be no different across that distance. i wil, run 10mm if need be, but whats your opinions on this? is a copper pipe in an outbuildiding a few m away any different to one that is 20m away in a larger house?

thanks

John
 
If the garage is attached to your house mate then as long as your main incoming water is bonded as per regulation 544.1.2 then it will be within your equipotential zone of the house.

The reason you need to bond back to the MET if you extend the zone to a detached building is the distance bewteen the main house and the out building, be it a couple of meters or 50 metres, is that the metal service if coming from the house, by the time it gets to the outbuilding can be of a different potential. You need therefore to make it the same potential as the house.

To be honest mate I would not put a non RCD protected socket in the garage, even if it is labelled and for test purposes. I would have no problem fitting a single non protected one next to the house CU. You may know what it is, and not plug something that can be used outside in it, but others may not.
 
If the garage is attached to your house mate then as long as your main incoming water is bonded as per regulation 544.1.2 then it will be within your equipotential zone of the house.

The reason you need to bond back to the MET if you extend the zone to a detached building is the distance bewteen the main house and the out building, be it a couple of meters or 50 metres, is that the metal service if coming from the house, by the time it gets to the outbuilding can be of a different potential. You need therefore to make it the same potential as the house.

To be honest mate I would not put a non RCD protected socket in the garage, even if it is labelled and for test purposes. I would have no problem fitting a single non protected one next to the house CU. You may know what it is, and not plug something that can be used outside in it, but others may not.

fair point malc. if i did have test socket, i would remove it when i move. putting one next to the CU is more hassle than its worth, as its in a kitchen cupboard, also wall space in there is very limited, and im gona be filling that up with switchfuse ect.

i know what your saying about the potential being different, but in reality? i suppose its worst case scenario (newbury?)
 
Last edited:
i agree with both points. like i said i will remove it when i move as the house is rented. in a normal situation i would not do this for a customer for the reasons malc stated, also id never forgive myself if ifound out somebody had fried on a lawnmower from my test socket. test failed!
cheers for the confidence spin, skilled is pushing it a bit! ;)
 
fair point malc. if i did have test socket, i would remove it when i move. putting one next to the CU is more hassle than its worth, as its in a kitchen cupboard, also wall space in there is very limited, and im gona be filling that up with switchfuse ect.

i know what your saying about the potential being different, but in reality? i suppose its worst case scenario (newbury?)

In reality john if your water mains is bonded, and the garage tap is fed from the house, and your taking the garage supply for the electrics also from the house, then I can't see as it's attached that your going to introduce that potential.

I assume that the spur for the tap comes of a kitchen/bathroom and just through the wall.

I remember the old Electricity Supply Regulations had a PME section and is was advised that in a PME, that even an outside tap should be sleeved when going through a wall or coming up from the ground, if fed from inside the house, but to be honest mate with RCD protection, bonding and the PME network so much more safer than 20 yrs ago I would think you are ok
 

Reply to attached garage in the Australia area at ElectriciansForums.net

Similar threads

  • Question
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
Replies
11
Views
2K
davesparks
D
I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top