Hi,
I'm looking for some guidance from more experienced hands. Have a friend who just bought a 2.2kw air compressor which is obviously blowing the fuse in the plug due to the start-up current. Manufacturers information suggests a 30a single phase motor DOL for the power rating whilst the person who sold it said it needs a 15a fused spur.
The compressor won't be installed on its own circuit with a type c circuit breaker so wondering what the best route to take given a fused spur off the ring is limited to 13a also? Someone suggested an unfused spur to a 16a single phase 2P+E connector and plug like you see at caravan parks which could cope with the start up current but any guidance much appreciated.
A little confused here, you say the manufacturer suggest fitting a DOL starter, doesn't this compressor already contain its own integral control?... or am I getting it wrong, a 2.2 kw single phase would have the effective inrush of a 5.5 to 7.5 kw 3ph so yes a 30amp front end type c would be recommended although you could use a permanent 16amp connection.
I agree but he sort manufacturers guidance which usually refines the worst case scenario those charts are based on. The higher the mcb the more problematic complying with ELI which makes advice difficult without having more info.
Try a 13A time delay (slow blow) fuse in the plug ? ?
I know this was said tongue-in-cheek but for those not familiar with fuse specs, normal 'slow-blow' cartridge fuses will not have the breaking capacity (nor will they correctly fit a 13A plug) and must not be used for this application.
Bedfordshire
United Kingdom
Trainee Electrician
Best way to connect up air compressor
Tbob27,
freddo,