Hi,

I'm looking for some guidance from more experienced hands. Have a friend who just bought a 2.2kw air compressor which is obviously blowing the fuse in the plug due to the start-up current. Manufacturers information suggests a 30a single phase motor DOL for the power rating whilst the person who sold it said it needs a 15a fused spur.

The compressor won't be installed on its own circuit with a type c circuit breaker so wondering what the best route to take given a fused spur off the ring is limited to 13a also? Someone suggested an unfused spur to a 16a single phase 2P+E connector and plug like you see at caravan parks which could cope with the start up current but any guidance much appreciated.
 
Based on the 30A fuse suggestion then it looks like a 32A C-curve MCB and matching circuit would be needed, either hard-wired to an isolator or a 32A commando style plug/socket (and of course RCD/RCBO use in that case, also if buried cables < 50mm, etc).
 
Could use a chunky VSD for less violent starting, though maybe not as chunky as this one that was connected to a 550KW fan motor...
VSD.jpg
 
SIngle phase motor driven air compressors like the one you mention most often use capacitor start and capacitor run type induction motors. For these motors, in order to have sufficient starting torque to quickly run up to speed without labouring the voltage at the motor terminals must not drop much. A consequence of too much voltage drop along the supply to the motor is a longer start time which will stress the start (and run capacitors) leading to reduced life. It is clear when they have failed when the motor fails to start and the overload trip operates through high stalled current - often the windings are damaged too because they have overheated.

As a for instance, my brother-in-law has a 2.2kW compressor in his workshop which was regularly failing. It was fed by a 30 to 40m run of doubled up 4mm2 singles - solution add in a third single for both L and N. If I remember correctly fed from a 32A type B mcb but would need to confirm this. I advised a new run of 16mm2 singles but we decided to see how triple 4mm2 singles performed first.

Do you volt drop analysis and calculations carefully. I cannot remember what the allowable voltage drop is for a CSCR motor driving an air compressor- someone will know. I think my BIL's run suffered 235 to 210V on start-up. (Of course some of this external due to Ze and he is fed by a pole transformer some 200m away).

See this:

Maximum voltage drop limit - Electrical Installation Guide - https://www.electrical-installation.org/enwiki/Maximum_voltage_drop_limit
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bedfordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Best way to connect up air compressor
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
20
Unsolved
--

Advert

Thread statistics

Created
Tbob27,
Last reply from
freddo,
Replies
20
Views
4,636

Advert

Back
Top