Just to add the ratings for IP protection are covered by:
  • regulation 416.2.1 for most areas at IP2X which basically is 12.5mm to prevent finger access, and;
  • regulation 416.2.2 for accessible top surfaces at IP4X which is 1mm access. Basically so if folks leave crap on the top of things it does not drop in to the enclosure.
The 1mm limit on the top is one often violated by open grommets, etc, that are otherwise safe from fingers.
 
Last edited:
  • Like
Reactions: LEighLeigh
Thank you again for all of the replies, very useful. In terms of the RFC he did mention that it was continuity, so reading through the comments it sounds as if the builders that moved the two sockets (one of which doesn't work) perhaps rewired them up incorrectly and I'm guessing this has caused the failure in relation to that C2 in which case hopefully an easy fix. The C2 on the CU, I can confirm there are certainly no 12.5mm gaps, the top surface I'm not sure, it's possible there is a 1mm gap I suppose, shame I don't live near the property. The shower light fitting not being IP rated for Zone 2 environments, I guess that just needs doing.
 
Overall it sounds like it will not be too expensive to fix. You can start by getting an estimate from the original electrician for the remedial work and if unsure then get another quote or two.

Also you can post it here for comments but with any personal information redacted (like the name/address for yourself, the electricians, or the rented property).
 
  • Like
Reactions: Jim_e_Jib
Overall it sounds like it will not be too expensive to fix. You can start by getting an estimate from the original electrician for the remedial work and if unsure then get another quote or two.

Also you can post it here for comments but with any personal information redacted (like the name/address for yourself, the electricians, or the rented property).
that's really useful, thank you!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
C2 issues? Consumer Unit & Circuit forms a Figure of 8 Rather than a complete RFC?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
LEighLeigh,
Last reply from
LEighLeigh,
Replies
43
Views
4,564

Advert