Hi guys,

struggling to work this question out and don't seem to be getting a correct answer no matter what cable conductor size i use.

Q. A 230V 14kW domestic electrical cooker, installed in a house is to be supplied by a 15m run of PVC insulated and sheathed cable, clipped to a surface. The cooker control unit has no integral 13A socket. The circuit is to be protected by a BS3036 fuse and the value of external impedance is 0.85 ohms. Calculate the minimum size cable that can be used for this circuit to comply with shock protection.

Ib = 14/230*1000 = 60.87A
In = 100A therefore max Zs = 0.53 ohms. ( i think)

Zs = Ze + [(R1+R2)*mf*L]/1000

Zs = 0.85 + [(1.83)*15] / 1000

Zs = 0.88 ohms ( too high)

using 50mm cable Zs = 0.85 + [0.387*15] / 1000

Zs = 0.86 ohms (still too high)

Feel im missing something obvious.
 
what he said^^^^. apply diversity and you get a design current of 27A
 