OP
Stu
[sorry didn't see page 2]
Hello again, doing this question too.
Step 1
Ref Method C clipped direct
Find Minimum size cable that will comply with shock.
Zs = Ze + ((R1+R2) x mf x L x 0.001
Zs = 0.85 + ((R1+R2) x 1.04 x 15 x 0.001
Zs of fuse must be greater than results from circuit.
Step 2
Ib = P/Uo = 14000W/230V = 60.87A
Using Diversity Table A1 OSG Cooker no Socket
Ib = ((60.87 - 10) x 0.3) + 10
Ib = 25.261A
In = BS 3036 type fuse
In = 30A (from table 41.2 with Zs of 1.09ohms
Therefore corrected cable size resistance value must 1.09ohms - 0.85ohms = 0.24ohms
Zs = 0.85 + ((R1+R2) x 0.156
Using Algerbraic Triangle to find 0.24ohms
0.24 = (R1+R2) x 0.156
0.24/0.156 = (R1+R2) = 15.38ohms
Therefore cables of values 15.38 or lower will comply with shock protection.
Table I1 shows Line conductor of 2.5mm2 with Protective conductor 2.5mm2 has a value of 14.82 and will comply
Hoping this is OK
Step 1
Step 2
Ib = 25.261A
Hoping this is OK