Hello again, doing this question too.

Step 1

Ref Method C clipped direct

Find Minimum size cable that will comply with shock.

Zs = Ze + ((R1+R2) x mf x L x 0.001

Zs = 0.85 + ((R1+R2) x 1.04 x 15 x 0.001

Zs of fuse must be greater than results from circuit.

Step 2

Ib = P/Uo = 14000W/230V = 60.87A

Using Diversity Table A1 OSG Cooker no Socket

Ib = ((60.87 - 10) x 0.3) + 10
Ib = 25.261A

In = BS 3036 type fuse
In = 30A (from table 41.2 with Zs of 1.09ohms

Therefore corrected cable size resistance value must 1.09ohms - 0.85ohms = 0.24ohms

Zs = 0.85 + ((R1+R2) x 0.156

Using Algerbraic Triangle to find 0.24ohms

0.24 = (R1+R2) x 0.156

0.24/0.156 = (R1+R2) = 15.38ohms

Therefore cables of values 15.38 or lower will comply with shock protection.

Table I1 shows Line conductor of 2.5mm2 with Protective conductor 2.5mm2 has a value of 14.82 and will comply

#####

Hoping this is OK
 
Last edited by a moderator:
In step one you have calculated the milliohms per metre value of the required cable not the Zs of the circuit and have not corrected the measured Ze to account for temperature (although the question may say this was measured at operating temperature)

In step 2 the 15.38 would therefore be milliohms per metre not ohms.
 

Reply to Cable selection, calculating earth fault loop impedance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
520
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
718
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Morning all. So just trying to refresh my grey matter but having a biff moment. Earth fault loop impedance with circuits protected by BS EN60898...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock