We're old fashioned and use tap mixers so no issue there, obviously something I'll need to know about.
Could you outline an install for me and I'll see if I can do the calcs?
 
10.5kw shower, 26.5m cable from board, 30deg ambient in loft, 150mm insulation, run inside stud Walls and clipped direct in the loft
 
Clipped under insulation or just vertically through?

Reckon it'll be tomorrow before I'm sober enough to do calcs.
 
how do you know , what percentage to apply for diversity in circuits. where do you's get this info from, sorry for hijackin. i know cooker is first 10A plus 30% thansk
 
think we do diversity tonmorrow at college, but dum dum left his books on the train, goneeeeeeeeeeeeeee and thanks
 
10.5Kw = 45.652A

No diversity applied, have taken it to be an instantaneous heater so 100% of load.

Ambient temp of 30c correction factor of 1.08
1.08 * 45.652 = 49.304

No conductor CSA specified but would need to be minimum of 10mm2 but with installation ref method 101 10mm2 is rated at 36A.

Using 16mm2 with ref method 101 allows 46A.

Me thinks you need to reroute cables and not under Insulation.

So go on, where did I go wrong?

 
You didn't, your calcs are spot on!

Realistically yes you would just change the method.

Let's have the vd calc then
 
I'll have a pop but couldn't see the mv/a/m anywhere for 16mm2 with ref 101.
Off to look in the big book.
 
what table does 1.08 come from for ambient air temp of 30 celcius?

And the formula for It is

It = Ib/(Ca*Cg* Ci* Cc) so that would be dividing not multiplying

Also table 6B of OSG or 52.2 of BRB is needed for the insulation to give you the factor for Cc

checkout p123 of OSG and tables 6A and 6B on the next 2 pages :)

edit - suppose could use method 101 for cable
 
Last edited by a moderator: