1.08 came from table 2e page 104 OSG.
Think I may be using the wrong table.

The formula you showed is for current carrying capacity, I got the max rated current from table 6f page 134 OSG. Is that wrong?
 
1.08 came from table 2e page 104 OSG.
Think I may be using the wrong table.

Yep you are using the correction factors for Zs

The formula you showed is for current carrying capacity, I got the max rated current from table 6f page 134 OSG. Is that wrong?

That is ok if you do it that way but if there are a variety of simultaneous factors you would have to work out It and then go to a table like 4D2A in the brb to select your cable size.

Table 4D5 of brb or 6F of OSG are fine if you can get a direct match to installation method.
 
So my calcs are ok for a simple installation?

What sort of simultaneous factors might arise?
 
two or more cables grouped together, higher ambient temps, running straight thru thermal insulation (had not read thru the method of installation, for your last example, properly when i commented initially) also could be on a rewireable to BS3036. You only use the worse case factors that are occuring at the same time. eg if it ran thru a metre of insulation and later the cable went thru a boiler house at higher ambient temp you would only use the insulation factor as that is the worst one and they are not occuring at the same time.
 
Cool, thanks.
Answers my question about multiple methods on same cable run. I assumed you should take worse case.

Will do bd calc in a while.
 
Here goes, assuming cable has now been sorted and is clipped direct for whole run.
Lb = 45.652
30c ambient correction = 1
mv/a/m for 10mm2 using ref method c is 4.4 -
(4.4 * 45.652 * 26.5) / 1000 = 5.323

So if now clipped direct 10mm2 t&e with 50a type b mcb will be ok

I think!
 
6mm2 has ccc of 46a with ref method c so thought 10mm2 better, but vd would be 8.831.

Sound about right?
 
Yeah it is a close run thing - 10mm on a 50A breaker gives lots of leeway and would be the sensible choice if you were installing. If, however, the 6mm cable was already in place and you were being asked to fit the 10.5kW shower you could just comply with a 45A mcb.

At 8.8V on the 6mm² the volt drop is still within 5% .
Hope this has helped a bit :)


edit : 4D5 of brb (the table for T&E) gives 6mm² at 47A
 
Last edited by a moderator:
Yes mate, it all helps.

I think I may have been using wrong table in OSG. Saying that I would still be happier installing 10mm on a 50a mcb.
 
Yes mate, it all helps.

I think I may have been using wrong table in OSG. Saying that I would still be happier installing 10mm on a 50a mcb.

yep - definitely agree when installing. Same with cookers makes sense to put slightly bigger cable in to leave scope for a future upgrade.
 