Presume you are doing a perodic?., then a PIR would suffice (or whatever the NICEIC choose to call theirs)
 
Went to do just this sort of job yesterday.
Customer called asking if I could issue a cert to proove that the caravan hadn't caused the small electrical fire on the site where it was stored :eek:, as the site owner said this van had caused the supply cable of the next van to burn out & catch fire :rolleyes: & had to be removed from the site asap & repair costs paid.
The site sparks said it had to be this caravan that was at fault because the rcd at the supply end had tripped :confused: & the state of the internal wiring just confirms his suspisions.
The most major of faults being that the main switch in the caravan (40amp 30mA rcd main switch + mcb's for circuit ocpd's) it is over rated at 40amp, this alone could cause major problems with all the wiring & is probably what is causing the rcd to trip :confused:.
All that advice & fault diagnosis given in the time it took him to smoke his smoke, he didnt even need to get a meter out apparently, all for the princely sum of £20.

Anyway I digress. So I Turned up & customer says " yes we bought it very cheap because it was owned by a squaddie in Germany & he had it rewired to use over here.

On the initial look around found:
(1) mix of sockets some were German shuko type others uk 3 pin.
(2) lights & sockets on same ocpd 10amp type C mcb
(3) all neutrals crimped together outside of small cu showing some bare conductors.
(4) scotch loc used to connect new cable to battery charger (+ve 24v) & its burnt out/melted
(5) cu & all cable joints located directly behind the gas fire (3" between them)
(6) uninsulated spades used for 230v termination into battery charger & no barrier
(7) charger left loose on the floor behind gas fire
(8) singles used for mains supply to charger, not enclosed & drapped over the gas pipe.

Starts to test;
(1) no cpc at any sockets, they have all been cut away.
(2) Gave up at this point & told the chap that I'd only charge for fuel used to get there & his best option would be to have the thing sorted before using it again.

I thought this was going top be such a simple ...bish bash bosh...heres the cert & invoice type job.:(
At least the compliment from customer was " thank you I appreciate the no bulls*** approch you have". :cool:
 
Nice Write up EasyFox. Its has put light upon a dark area in my experience. So i guess this is not a straight forward inspection that i anticipated but i guess it going to depend on the age of the caravan. So i think i might give it some time as i fancy something a liittle different might be fun.

Thank s Marty
 
My way of testing a caravan is to put a lump of plastic explosives under it and set it off.:eek:

The test would then be to see how high you can get it and into how many pieces.:p
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Caravans ??
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Ts1 Marty,
Last reply from
Moog,
Replies
7
Views
2,588

Advert

Back
Top