"Said fuse went again today and in the process of rewiring it, I noticed that there was no power to any of the british gas kit or their immersion heater - the inlaws hadnt noticed this before......It transpires that the kit and the immersion heater is running off a 5A lighting circuit."

He seems to have cleared this up!
 
sounds like the C/H controller is the problem, overloading the lighting circuit when lights are on. as said before, immersion heater would blow a 5A fuse pretty rapid. good job they not a farmer or a nail would have replaced the fuse the first time it went.
 
The controller being on the lighting circuit NOT the immersion.


When the lighting circuit fuse is removed, there is no power what so ever to the immersion and Ive not had a go at trying to fathom why, but it stands to reason that some, if not all of its power is being drawn from the lighting circuit.I don't know the details of the immersion, Ie its power, I only know that, according to the occupants, its the same one thats been in since they moved in, around 30 years ago. I only became privy to this issue a matter of hours ago and wanted some second opinions.
 
I can assume that the central heating is the primary source of heating and hot water and the immersion heater is there as a back up , so if the 5amp fusewire is blowing when the lights and c/h ssystem is in use then there is an overload , meaning the c/h system needs to be on its own circuit , to put it bluntly if B G put the system in its their responsibility to put in the correct circuits regardless of solid wood floors and the difficulties , after all they would have had to do find a supply for the immersion heater circuit
 
I can assume that the central heating is the primary source of heating and hot water and the immersion heater is there as a back up , so if the 5amp fusewire is blowing when the lights and c/h ssystem is in use then there is an overload , meaning the c/h system needs to be on its own circuit , to put it bluntly if B G put the system in its their responsibility to put in the correct circuits regardless of solid wood floors and the difficulties , after all they would have had to do find a supply for the immersion heater circuit


Makes sense to me. There is an accessible socket considerably closer to where the dam thing is mounted than any live feed from the lighting, and unless they know something I don't, it would have been 'easier' to take the feed off.


Anyway, thanks to all for the feedback
 
Makes sense to me. There is an accessible socket considerably closer to where the dam thing is mounted than any live feed from the lighting, and unless they know something I don't, it would have been 'easier' to take the feed off.


Anyway, thanks to all for the feedback
If your saying your lighting is pulling 3 amp your boiler would not be overloading that circuit, you are being tunnel visioned into looking for the overloading problem. Moving onto the ring will not sort this problem, I'd be looking for a cable that has been damaged during boiler installation. Or something along them lines. Possibly a cable trapped under a hot pipe that is breaking down the insulation when the heating pipes warms up then when they cool down the insulation hardening again that's why you can replace the fuse wire. I only say this because that is a fault I came across recently but it could be numerous different scenarios.
 
If your saying your lighting is pulling 3 amp your boiler would not be overloading that circuit, you are being tunnel visioned into looking for the overloading problem. Moving onto the ring will not sort this problem, I'd be looking for a cable that has been damaged during boiler installation. Or something along them lines. Possibly a cable trapped under a hot pipe that is breaking down the insulation when the heating pipes warms up then when they cool down the insulation hardening again that's why you can replace the fuse wire. I only say this because that is a fault I came across recently but it could be numerous different scenarios.


Its quite possible that what you say has occurred, and I have no reason to disagree, but I wouldn't say I'm being tunnel visioned into an overloading problem, its just that given the circumstances mentioned earlier on in this thread, an overloading problem appears to be a distinct possibility, so its worth looking into. I also have plans to test and inspect the entire house as it hasn't had anything done to it for years and I imagine it could do with a rewire. Before that, BG need to come back and fulfil their obligations.
 
I would tend to go with the idea that BG have caused some sort of short. For it to be an overload that is an lot of lights being on. This controller should take less than 500mA.
How was the fusewire ruptured? An overload would tend to be a break in the fusewire, you may even see a blob of copper on one leg of the blown fuse, where a fault current would tend to destroy the fusewire.
 
You also need to take into account that the Controller Switches the pump on.
This does take a couple of Amps on startup.
Go for the FSU off ring, safety first.
Rgds.
 
Just ran my combi boiler and clamped it, pump running fan running and ignition. It was ........................0.1A
 
Just ran my combi boiler and clamped it, pump running fan running and ignition. It was ........................0.1A

I would suggest putting your MM in line as most go up to 10A and then check otherwise we would all like a boiler like yours running at 0.1A, WOW !.
Rgds.
 
Just ran my combi boiler and clamped it, pump running fan running and ignition. It was ........................0.1A

I suggest you should contact an expert to check up the damage and fix it as well. That could be the safest and the best solution you should consider to solve your problem. Rather than fixing it by yourself, that could be too risky!
 
I would suggest putting your MM in line as most go up to 10A and then check otherwise we would all like a boiler like yours running at 0.1A, WOW !.
Rgds.

10A! I live in a house not a boiler room. It is protected by a 3 amp fuse. You must have a fooooooooooookin massive boiler or a fooooooooooooookin massive nose .
 
Just a thought, and can't say I've ever seen it done but maybe the immersion is the primary source of hot water and they are using the C/H programmer as a control through a relay/contactor, this would explain why there would be no power at the immersion point when fuse has blown, although doesnt answer WHY the fuse is blowing.
 