Hi Guys just replaced a 200 amp main isolator in a factory along with a replacement 3 phase board should you do an installation cert or a minor works as it's like for like
 
Before we start anything like this we like to get as much information eg existing certificates, circuit charts etc and turn off each circuit to prove what it feeds so when reinstalled we know what it does for retesting and is safe to bring back into service.
 
Got the old certs for the board mainly concerned about the main isolator I'm tempted to issue a minor works for it but would any one issue different
As Westward10 (who beat me to it while I made a cup of tea) posted I would do an EIC this is more than minor works you have the circuits in the distribution board to consider. You are required to put this information on the certificate anyway.
 
You need an Electrical installation certificate for the new board and all finals circuits within, plus the new isolator.

All tests will be from an initial verification prospective and will include all tests performed in the sequence stated.

Apologies if I'm telling you how to suck eggs
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cheshire
Business Name
Stay Switched On

Thread Information

Title
Certificate for replacing a main 200amp isolator
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
Daveh36,
Last reply from
BruvDunk,
Replies
18
Views
2,712

Advert

Back
Top