Can someone tell me about cooker cables, the in-laws have had a new kitchen fitted, but they have put the cooker on 2.5mm cable, and wired it in to the ring main off a switched fuse ???
the cooker is a range master, for some reason the kitchen fitters took the manual for the cooker ???
but I have download a copy, it states that with both ovens, clock and grill it's 7.5kw (the hob is gas)
the reason I ask is because on Saturday had family party, used the ovens and the fuse blown, not much fun when your half way cooking, I always thought cooker cables are 6mm.
the manual does say 2.5mm to 6mm but to me the lines point to the cores in the cable, if that makes sense
 
Welcome to the forum .. I've approved your thread for general forum for speed of response as your only asking advice, when admin is on line you will be assigned a DIY status.

Be gentle boys he only asking if it's done wrong.
 
image.png Added a screen shot from a page in the manual, the cooker looks the same but as the kitchen fitter took the one that comes with it, I can't be 100%
 
Cooker can be connected utilising a 3phase supply and removing the bridge at the connections on the cooker which in turn a smaller csa of cable could be used hence the minimum of 2.5mm which you mention. As you probably don't have a 3 Phase supply then ideally a 6-10mm cable should of been installed for the cooker back to the consumer unit.
 
I personally would not allow the idiot to come and attempt to rectify it. A nominated registered electrician selected by him yes, but the original person that put that cooker on to the ring circuit, no way.

You need a separate cooker circuit installed which is notifiable and you should be getting a installation cert and compliance cert.

A big question is whether this cooker was always going to be the one installed, as this will effect whether you have any recourse to the company. If they quoted based on this cooker being installed the work should have entailed a new circuit and upgrading to bonding as necessary.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Cooker cable
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
35
Unsolved
--

Advert

Thread statistics

Created
Anthony16090,
Last reply from
telectrix,
Replies
35
Views
6,314

Advert

Back
Top