use good european pv low power loss dc cables 4/6mm2
most are not very good quality look for tuv specs and designed for 25/30years lifespan
keep dc runs short as possible 10metre is good practice
you could try mounting the inverter & dc isolator outside most goods ones are waterproof IP65

Why limit Dc cable run to 10 metres?
 
to lower power loss and keep yield of system as high as possible
600/1000vdc quite dangerous in domestic roofs/attics/garage
eg in event of a fire during daylight unless pv fireman switch is used or rodents/children damaging conductors
good pv cable eg 4mm2 low power loss - 55amps 1800vdc - halogen free - cross linked - uv resistant for 30years & very high short circuit proof
on pv parks/trackers inverters are mounted directly onto the back of the racks and dc converted to ac as quick as possible
 
to lower power loss and keep yield of system as high as possible
600/1000vdc quite dangerous in domestic roofs/attics/garage
eg in event of a fire during daylight unless pv fireman switch is used or rodents/children damaging conductors
good pv cable eg 4mm2 low power loss - 55amps 1800vdc - halogen free - cross linked - uv resistant for 30years & very high short circuit proof
on pv parks/trackers inverters are mounted directly onto the back of the racks and dc converted to ac as quick as possible

Valid points above

any voltage present in Ac or Dc circuits is dangerous and a fire risk and I do think that the firemans switch is a good idea

However if installed correctly I see no reason why you can't have longer runs
Also on large pv systems ie >100kw it is common practice to run the dc from the arrays as far as 70 metres to central inverters, I realise this is not the same as a domestic install.
If the installer has thought about this and is implementing sensible practices and installation methods following the regs then how can it be viewed as a bad practice
I would argue that putting the inverter in the attic is though.
 
pv fireman switch used in germany/continent generally on commercial systems to remotely isolated the system
no problems using longer runs as long as its good pv low loss cables
problem most suppliers/wholesalers supply the cheap stuff

nb you have to take in to account 95% of mcs installers where installing windows or kitchens last year
power loss , cable runs . best practice mean nothing to them
had one that installed a 4kwp ground system with 200metres dc cable runs !! and one that fitted a indoor inverter outdoor on a roof
most have have no electrical background , usually buying from the lowest bidder

n
Valid points above

any voltage present in Ac or Dc circuits is dangerous and a fire risk and I do think that the firemans switch is a good idea

However if installed correctly I see no reason why you can't have longer runs
Also on large pv systems ie >100kw it is common practice to run the dc from the arrays as far as 70 metres to central inverters, I realise this is not the same as a domestic install.
If the installer has thought about this and is implementing sensible practices and installation methods following the regs then how can it be viewed as a bad practice
I would argue that putting the inverter in the attic is though.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
D.C. Cables
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
18

Thread Tags

Advert

Thread statistics

Created
Elysium,
Last reply from
daytona600,
Replies
18
Views
6,034

Advert

Back
Top