I wish I hadn’t taken the cover off now….

New customer. Lighting fault, breaker would reset, 4 or 5 times… then wouldn’t reset at all, and tripped with a crack.
Boiler is also off this lighting circuit so I’ve ran a temp supply for that just now.

Reading 5Mohms and rising on L-E and N-E.
Suspect circuit is second from left and disconnected for now.

Other issues with board include inner cores of flex on left most breaker supplying bell transformer (no bell) into exposed connector block. Took that out straight away.

There’s so much excess copper on show.. and no idea with the black going into a breaker.
Neutrals don’t correspond with lines and this was supposedly rewired in 2002.

D231B65A-E6E2-4F5E-A31B-F472CC81C0C8.jpeg



I’ll get all the faults sorted, then get some rcbo’s for it.
 
This might confuse a DIYer...either the label is on upside down, or the cables are reversed on the tray...
It works though, now!
I apologise for the state of the ferrules, they were re-done once I had the unit running.
 
So bad you posted the image twice.
 
Like New York, so good they named it twice!
Listen, I'm hopeless with posting stuff, so My apologies!
 
This might confuse a DIYer...either the label is on upside down, or the cables are reversed on the tray...
It works though, now!
I apologise for the state of the ferrules, they were re-done once I had the unit running.

I've seen this with cheap lights bought from Amazon, one of which stated on its product page that blue was line and brown was neutral. That one was handed to the guy that bought it, with clear instructions about what he could do with it.
 
Indeed, @nicebutdim
I had an accessory recently where the wiring instructions were written step-by-step, and there were illustrations too...problem was that they conflicted. OK for me to sort out what was what, but anyone following the diagram would end up with a blown timeclock. I contacted the manufacturers, they thanked me for being in touch, and said they would review things...
Aye, right...as we say in Scotland.
 
Tom Jones greatest hits perhaps?
 
  • Funny
Reactions: Sapper
Bathroom light was wired directly into the shower isolator. Neutral burnt out and insulation shot on shower circuit. 40 year old board with no RCD protection, so that’s added to the quote too.


D3A71454-1359-4A3E-B8E9-082F6ACDE233.jpeg
 
Installing some outside sockets today and notice that their EV charge point was fed with ordinary SWA. It piqued my curiosity as I also do EV charge points and know they have to have active load management. Along with OCPD & RCD protection, though some are now starting to come with both 6mA DC & 30mA protection built in. The charge point installed has neither OCPD or 30mA protection built in. Just 6mA DC.

As there was no seperate cable for the CT clamp and they weren’t using EV ultra/Hyper Connect I quizzed the owner on where the supply for the charge point was.

Now there are a number of plethora of ‘issues’ here.

But I have circled the supply to the EV charge point. The main cutout rating is also only 60A.

Funny enough they didn’t have a certificate for it and I’m betting the DNO haven’t been informed.

Customer tried to get hold of installer whilst I was there but the no. was switched off. So I’ve left him with all the details of how it should be done. So he can quiz the installer. He asked if I could rectify it all which I said of course. But he should approach the installer first as they should rectify it FoC.

E5AF48D0-938D-439D-A3DE-69F1A0DA27E0.jpeg
 
Now there are a number of plethora of ‘issues’ here.
Indeed, but the oddest to me is why saw the right end of the MET? Not that the left end is being used for a fixing screw!
 
Indeed, but the oddest to me is why saw the right end of the MET? Not that the left end is being used for a fixing screw!
Who knows? I often wonder when I see stuff like this if they were pi55ed!
 
Oh joy of joy!

IMG_0018.jpeg
IMG_0016.jpeg
 
Earth 2nd from top is very cute.
 
There’s pyro in there as well!
Easily damaged with the pot and seals protruding in like that.
 
There’s pyro in there as well!
Easily damaged with the pot and seals protruding in like that.
Whole house was originally wired in Pyro. The T&E as later circuits. Given him a huge price for updating the board and he's accepted!
 
  • Like
Reactions: timhoward and DPG

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Dodgy trade pictures for your amusement! - 1 Million Views!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8K

Advert

Thread statistics

Created
Darkwood,
Last reply from
mainline,
Replies
8,099
Views
1,258,981

Advert