Just the first paragraph.
Reg. in question is (as someone else mentioned) to cover the likes of borrowed neutrals.
I have always designed domestic lighting installs so that if one light is out, then the next is not only on a different MCB, but on a different RCD as well. For instance, on a first floor, all the rooms would be on one or more MCBs, but on the same RCD, and the passage/stairs light would be on another RCD.
On the "more than one circuit into one MCB" argument, I consider it good design to bring lighting circuits near the consumer unit back separately and into the same MCB because of the help it gives to fault finding.
The very last fault finding job I did was to sort a s/c on a lighting circuit, and there were three "circuits" originating from the same MCB, affecting considerable part of the house. After a couple of minutes testing at the consumer unit, I was able to reinstate all but couple of utility room lights, which were left to the following week.
 
I don't believe it's a regulation, but it is suggested that you leave a percentage of spares. Last one I did, it got 2 spares for 8 circuits. I can't remember the percentage though.

As for the question from @Jjc about identifying which cable is which... as @anthonybragg said... label it :) Simples :D And if that hasn't been done, used some basic fault finding techniques to identify it... link L-E on one, N-E on the other and a quick continuity check will establish which is which.... then you label it.
Yes I know all about circuitry and tracing circuits what about three phase boards if for some reason someone connected one of the two cables into a breaker
on a different phase? We are not talking simple domestics now.
 
Yes I know all about circuitry and tracing circuits what about three phase boards if for some reason someone connected one of the two cables into a breaker
on a different phase? We are not talking simple domestics now.

Then it's two separate single phase circuits supplied by two separate OCPD in a three phase board.
 
I think the regulations recommend that consideration be given to foreseeable future expansion to the installation somewhere near the beginning of the book.
I may be recalling this from previous editions though.
 
BYB Definitions

Circuit. An assembly of electrical equipment supplied from the same origin and protected against over current by the same protective device(s)

314.4 Where an installation comprises of more than 1 final circuit, each final circuit shall be connected to a separate way in the distribution board ....

Neither of these state that a final circuit only has 1 cable

so............ I would say that the OP's original circuit complied 100%

Or the OP could have whipped out a short length of T&E, plus some Wago's and joined the 2 cables just before the MCB and then what
 
New posts

Reply to Does this setup contravene any regs or is it ok? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top