should you install a earth rod if running a feed to a shed which is built on timber frame and is all timber , no metal parts and will have no services ie gas or water in it so no need for bonding only a supply for a light and a couple of sockets or can you use a pme earth from fuseboard if the shed supply is run in 6mm armoured from the outside of the house ( inside house 6mm t+e to fuseboard ) protected by 32amp rcbo will be installing a 2 way board with rcd main switch in shed approx 25 meters away
 
What’s the earthing arrangement at source?

Have you spoken to your CPS tech helpline?
 
As Mudroch and Des mentioned don't install two30ma Rcds in line with each other and why use T&E how are you running it outside ?, I Would use Swa and so there will be no nead for a rcd at the supply end
 
Hi Tim- The means of earthing at the installation origin can be used at outbuildings, but it does have to be designed. IET Guide Note 8 has some useful "how to" examples.
 
What scheme is that? Whenever I rung Elecsa tech helpline, they never asked me anything to verify membership.
Stroma
As Mudroch and Des mentioned don't install two30ma Rcds in line with each other and why use T&E how are you running it outside ?, I Would use Swa and so there will be no nead for a rcd at the supply end
I’m running swa outside from the house to shed terminating into a wiska box then t+e in cupboard in trunking up to ceiling then will be clipped in ceiling void , before dropping back down to fuseboard which is cupboard under the stairs client doesn’t want any chasing
 
New posts

Reply to Earth rod needed for shed supply or pme allowed ???? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
569
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
532
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Replies
3
Views
291
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
535

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock