should you install a earth rod if running a feed to a shed which is built on timber frame and is all timber , no metal parts and will have no services ie gas or water in it so no need for bonding only a supply for a light and a couple of sockets or can you use a pme earth from fuseboard if the shed supply is run in 6mm armoured from the outside of the house ( inside house 6mm t+e to fuseboard ) protected by 32amp rcbo will be installing a 2 way board with rcd main switch in shed approx 25 meters away
 
  • Like
Reactions: DavLa2009
Rod not necessary
Whats the score with the 2 Rcds?
 
Have you spoken to your CPS tech helpline?

That helpline is technically only to help them obtain payment from a bank account!
 
  • Like
Reactions: Colin33 and Strima
The earthing arrangement is pme , in process of joining cps scheme tried ringing for advice and they said they can’t give me any advice as not member yet

What scheme is that? Whenever I rung Elecsa tech helpline, they never asked me anything to verify membership.
 
  • Agree
Reactions: 1 person
As Mudroch and Des mentioned don't install two30ma Rcds in line with each other and why use T&E how are you running it outside ?, I Would use Swa and so there will be no nead for a rcd at the supply end
 
  • Like
Reactions: DPG
Hi Tim- The means of earthing at the installation origin can be used at outbuildings, but it does have to be designed. IET Guide Note 8 has some useful "how to" examples.
 
  • Agree
Reactions: 1 person
What scheme is that? Whenever I rung Elecsa tech helpline, they never asked me anything to verify membership.
Stroma
As Mudroch and Des mentioned don't install two30ma Rcds in line with each other and why use T&E how are you running it outside ?, I Would use Swa and so there will be no nead for a rcd at the supply end
I’m running swa outside from the house to shed terminating into a wiska box then t+e in cupboard in trunking up to ceiling then will be clipped in ceiling void , before dropping back down to fuseboard which is cupboard under the stairs client doesn’t want any chasing
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Earth rod needed for shed supply or pme allowed ????
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
102

Advert

Thread statistics

Created
Tim collins,
Last reply from
Nigel,
Replies
102
Views
34,014

Advert