Just a note as the title is somewhat ambiguous, the PME arrangement stops at the cutout, we do not export or extend PME normally as that would need to be agreed with the National Grid guys, I sense you didn't mean this, the PME or other arrangement at source can effect though your own earthing arrangments which will be a TNS format or a TT or a mixture.
If you ever have a PME or TNCS at source then you have a very sound reliable earthing system and regardless how the outbuilding is arranged I would always use the provided earth and if needed then bring an equipotential bond out... I would only consider TTing the out building to reduce costs on a bigger scale but there would need to be a very large distance to be covered to justify this IMHO. TT systems are inherently variable so getting a constant reliable good earthing reading is difficult as your readings are easily effected by the conditions on the day.