Seriously wire puller are you pulling my leg, how much heat is produced from a sealed boiler a lot less than a radiator. So in that case we will have to put the con unit outside.
 
I'm not saying that installing a CU in the same cupboard as a boiler is a complete No No, but it certainly wouldn't ever be my choice of locating a CU. If anyone here thinks a boiler in a closed cupboard isn't going to increase the ambient temperature within that space, needs to think again. And ambient temperature can/will have an effect on the CU's protective devices...
 
Seriously wire puller are you pulling my leg, how much heat is produced from a sealed boiler a lot less than a radiator. So in that case we will have to put the con unit outside.

Dont pull legs mate....clues in the title:redface:


Anyway......older boilers produce a lot morre heat than modern ones,ambient temperature may be an issue to be taken into account in some circumstances.
 
If anyone here thinks a boiler in a closed cupboard isn't going to increase the ambient temperature within that space, needs to think again. And ambient temperature can/will have an effect on the CU's protective devices...

Agreed, but a modern condensing boiler produces a remarkably small amount of 'waste' heat from the casing.
 
and if the ambient tempreture rises above 30*....as its likely to do next to a heat sourse in a confined space....
 
Hello,

I have just moved into a new house, which will require a full rewire.

I am looking at relocating the main electrical consumer unit into the boiler room which houses the gas combi boiler.

Can anyone advise any regulations that would resrict this?


Thanks,

Callum


"Hello Callum",

PLEASE don`t think that I am being funny with this - but for other less Professional readers:

I would definitely advise that You do NOT fit the Consumer Unit in a position where a leak from the Boiler or any associated Controls - Pump / Zone Valves etc. could drip onto it.

Obviously you would definitely NOT fit the CU Under the Boiler / Pump & Zone Valves for that reason.

You would be surprised at where I have seen Electrical Consumer Units in relation to Boilers / Heating Equipment.

Regards,

Chris - Heating Engineer / Gas Engineer.
 
You would be surprised at where I have seen Electrical Consumer Units in relation to Boilers / Heating Equipment.


A switch can be sited behind a door,it's never the door hung incorrectly
So with that in mind Chris,Can I remind you,in these cases,the heating always came after the electrics
:sifone:
 
You would be surprised at where I have seen Electrical Consumer Units in relation to Boilers / Heating Equipment.


A switch can be sited behind a door,it's never the door hung incorrectly
So with that in mind Chris,Can I remind you,in these cases,the heating always came after the electrics
:sifone:


"Hello Des 56",


MOST of the examples that came to My mind were where the Consumer Units had definitely been installed AFTER the Boiler / Pump / Zone Valves - on the majority of those I could tell that was the case by just looking at the Heating Pipework in relation to the Electrical Wiring / Trunking etc.

I am definitely Professional enough to be able to have made that kind of Judgement / Assessment of the situation.

I have often worked on Refurbishment Works where the NEW Electrical Work is carried out AFTER / During Me installing the Heating and Plumbing to a Property - Electricians who knew Me [and some who did not] liked to come in AFTER I had taken up loads of Floorboards throughout the property.

Although obviously they would NOT be running cables under the same Boards as My Pipework they could use My Boards for accessing across Rooms and adjacent Boards for some cable runs.

SO IT IS NOT ALWAYS THE CASE THAT THE `NEW` ELECTRICAL WORK / CONSUMER UNIT COMES FIRST !


I would have thought that My previous Posts on this Forum would have shown that I have the greatest respect for the Electrical Profession / Electrical Professionals - So My comment that You quoted was NOT a `Dig` at Electricians.

The examples of Consumer Units that I remember were in totally inappropriate positions in relation to Heating Boilers and equipment and I would have been VERY surprised if they had been installed by Professional Electricians.


"Happy New Year Des",


Regards,


Chris
 
Last edited:
Chris please,not for one moment was there meant to be anything serious about the post,it was indeed a failed attempt at humour by me that's definite

Your previous posts and the info you give has been invaluable to many and long may it continue
You have my sincerest apologise for any offence created

:innocent: :sailor:
 
Chris please,not for one moment was there meant to be anything serious about the post,it was indeed a failed attempt at humour by me that's definite

Your previous posts and the info you give has been invaluable to many and long may it continue
You have my sincerest apologise for any offence created


"Hello again Des",


Thanks for your latest message - I was Editing My Post while You were writing it.

I did wonder if I had irritated You - and I did not mean what I originally wrote to state that an Electrical Professional had carried out ANY of the examples that I eluded to - the Works were almost undoubtedly done by `Cowboys`!

Sorry that I did not realise that You were having a Joke - Please don`t be offended by My Edits to the reply to You - I was trying to `Defend Myself` while also being hopefully inoffensive to You.


Again - "Happy New Year to You and your Family Des".

Regards,

Chris
 
Hi guys....thanks for your comments.

Glad everyone are now friends again...

I'll keep you updated with the outcomes of CU positioning & overhead supply change in the new year!!
 
Hi guys....thanks for your comments.

Glad everyone are now friends again...

I'll keep you updated with the outcomes of CU positioning & overhead supply change in the new year!!


"Hello Callum",


I was not suggesting that You would install the Consumer Unit in an inappropriate place by what I wrote.

I was writing My comments for the benefit of Non - Electricians who might find your thread and need advice about what NOT to Do / have done regarding positioning the CU.

Sometimes what We know to be `Obvious` does NOT occur to perhaps a person who wants to move Electrical or Heating / Plumbing items etc. - while doing a refurbishment for example.

And although their Contractor / Professional Tradesman should NOT install ANY Item in an inappropriate position - reading NOT to do something is often a good start to the `Thinking process` prior to any planned Works.


"Happy New Year Callum",

Regards,

Chris

- - - Updated - - -
 
"Hello Callum",


I was not suggesting that You would install the Consumer Unit in an inappropriate place by what I wrote.

I was writing My comments for the benefit of Non - Electricians who might find your thread and need advice about what NOT to Do / have done regarding positioning the CU.

Sometimes what We know to be `Obvious` does NOT occur to perhaps a person who wants to move Electrical or Heating / Plumbing items etc. - while doing a refurbishment for example.

And although their Contractor / Professional Tradesman should NOT install ANY Item in an inappropriate position - reading NOT to do something is often a good start to the `Thinking process` prior to any planned Works.


"Happy New Year Callum",

Regards,

Chris

- - - Updated - - -

Hi Chris, I see you updated your post. No offence taken - I knew where you were coming from.

Not to worry anyway.....deceiced to have the Gas Boiler relocated to the loft so the CU can go where I like (within reason!!)

Thanks again to all the helpful posters...
 
Hi Guys, Thought I would update the thread.

Dug the pipe trench and laid the duct at the weekend for my new underground supply. Had Scottish Power round earlier in the week to install 30m new underground cable and joint this onto the cable that fed up the pole orginally. Just waiting on the linesman coming to remove the overhead cables and pole. All Good that end!

Ended up putting the boiler in the loft which has given us more space!! I have just decided to have the new CU mounted in the same location once it comes to rewiring the full house.

Cheers, Callum
 