Hi people,
Need your advice recently wired an electric oven onto new twin rcd board.
Oven was working on previous rcd and was recently purchased about a week a go. Was working fine on old type cartridge fuse board [emoji33] .
When I did insulation reading it would fail when I turn isolator on and test. So I checked all the wiring, removed oven and tested on a temporary plug and no tripping occurred.
Connection is fuse board to double pole isolator with 6mm to outlet plate and then oven.
I then removed isolator and placed connector block I got readings of around 35mega ohms on 250v.
After which I found the neon on the on side of isolator was causing ir fail removed and tested all passed ir so connected to 40a breaker as soon as isolator is turned on the rcd trips even before the oven is switched on.
Then an rcd ramp test was performed and was satisfactory.
My suspicion are 40a mcb or double pole isolator open to suggestions or further tests ?
Have I missed anything ?
Need your advice recently wired an electric oven onto new twin rcd board.
Oven was working on previous rcd and was recently purchased about a week a go. Was working fine on old type cartridge fuse board [emoji33] .
When I did insulation reading it would fail when I turn isolator on and test. So I checked all the wiring, removed oven and tested on a temporary plug and no tripping occurred.
Connection is fuse board to double pole isolator with 6mm to outlet plate and then oven.
I then removed isolator and placed connector block I got readings of around 35mega ohms on 250v.
After which I found the neon on the on side of isolator was causing ir fail removed and tested all passed ir so connected to 40a breaker as soon as isolator is turned on the rcd trips even before the oven is switched on.
Then an rcd ramp test was performed and was satisfactory.
My suspicion are 40a mcb or double pole isolator open to suggestions or further tests ?
Have I missed anything ?