Having our 1930's flat re-wired and re-plumbed. Floors and ceilings are concrete - so wires and pipes are all being chased into walls!

Radiators are currently set very high and have asked for them to be lowered to a standard height - however the electrician is putting the wiring around from socket to socket at a height of approx 10-12 cm and I'm uncertain how the plumbing will be set. Has the electrician left room for the pipes to be set below the wiring - otherwise the rads are not going to be very much lower - unless there is a way of doing this!?!? Can someone help me with the logistics of this - I don't know how everything works!!!

Also - the wiring is being covered with metal capping - I'm guessing this is safe just below/behind a radiator and close to heating pipes??

Electrics 1.JPG Electrics 2.JPG Electrics 3.JPG
 
So the electrician is not bothering running wiring in prescribed zones then ?

That aside, buried cables under capping and plaster should not suffer greatly from the effects of being close to a radiator.
 
Where cables of that type are buried less than 50mm from the surface they must be installed in zones that are formed by the corners of walls and ceilings or in horizontal and vertical zones from accessories. The diagram in the link shows it better.
Where zones are not used the cable (of this type) can be given mechanical protection suitable to prevent nails and screws penetrating. The metal capping used does not provide this protection.

All that said I can't see there being many problems in the future with accidental cable damage, but the runs on walls with no sockets are probably the biggest hazard.

 
what andy says. horizontal cables must be fixed directly in line with the sockets. (not down, across , and up).
1569064268060.png

even then. wet-pants will be sure to drill them.
 
OK - so, where there is a socket on the wall they can go horizontally across the wall at that height - but on a wall with no socket they need to go up, across near the top and then down again - is that correct?

If they are in
[automerge]1569064650[/automerge]
Where zones are not used the cable (of this type) can be given mechanical protection suitable to prevent nails and screws penetrating. The metal capping used does not provide this protection.


What should they be using for this wiring where they have put it?
 
OK - so, where there is a socket on the wall they can go horizontally across the wall at that height - but on a wall with no socket they need to go up, across near the top and then down again - is that correct?

Yes

What should they be using for this wiring where they have put it?

Not entirely sure as I've never done that, but I'm certain that products exist

I bet your sparky hates this forum by now.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
High Wycombe
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
If other, please explain
Homeowner

Thread Information

Title
Electrical Wiring vs Plumbing
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Suet33,
Last reply from
Andy78,
Replies
6
Views
1,597

Advert

Back
Top