I dont disagree up to a point and I think you will find Skelton doesnt either.
The issue constantly raised by us is that many who scoff at the Bs7671 max values appear to be happy with values which will still not operate an OCPD in a reasonable time, if at all.They are still reliant on an RCD.
Given that a value of 10 ohms or 200 ohms......or even 1667 ohms will make no difference to RCD trip times why aim for a lower value unless you get TN values?
Using your argument, One could easily ask WHY would you be giving a dam about Zs values on a TN system, if your both so confident that an RCD will ''Always'' fulfill your Zs requirement to trip the OCPD?? That argument (which i also disagree with) is just as valid as you blindly accepting a 200 ohm Ra on a TT system because a Reg vaguely say so ...
As i've stated many times here, if i had installed a rod position that gave me a 10 ohms value, another rod would ''always/automatically'' be added, you have would to be a bloody fool not too!! And yes, it is more than possible in many instances to achieve near TN values, but that takes a bit of time and effort and knowing what your doing. But again, that's something else that has been lost in time and space!! lol!!
Yes you can get over situations with the use of RCD devices, but at the end of the day, it is just a substitute, it's not really a valid TT system, even more so if you haven't even tried!!! I've been involved with far, far too many TT systems of every type and description, in various countries and locations, that you'll ever convince me in the slightest, that a rod with a 200 ohm Ra sitting on it, is any sort of a TT system. What it is, is a bloody joke!!
Encouraging these younger sparks and untrained so-called DI's, to not even bother installing a decent TT system and just bung an RCD in, isn't the message we should be portraying either!!