bobsteroo
just installed cooker cct, rcd fuse box,earth bond main services etc. tested ze which was 0.02ohms
and the pfc reading was 12.2 ka which i thought was very high, i asked a few electricians
at wholesalers what they thought, no one has had a reading like that, i have borrowed a mates meter, tested the cable again with a similar reading. i have been back 3 more times and the reading varies from 11.6 to 12.2 ka. i have phoned united utilities and told them they said they are only concerned mainly about the ze and they are happy with 0.02 ohms.
the mains is a tncs will this be acceptable if i issue a wiring completion cert and make a note that united utillities have been informed.
i have changed the m.c.b to a 10 ka [capacity] any advice would be helpful thanks
and the pfc reading was 12.2 ka which i thought was very high, i asked a few electricians
at wholesalers what they thought, no one has had a reading like that, i have borrowed a mates meter, tested the cable again with a similar reading. i have been back 3 more times and the reading varies from 11.6 to 12.2 ka. i have phoned united utilities and told them they said they are only concerned mainly about the ze and they are happy with 0.02 ohms.