Hob combustable zone and socket outlet

Discuss Hob combustable zone and socket outlet in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
36
Hi all
as the picture attached you can see the location of the hob and the metal socket to the right, now the gas fitter has gone to commission the gas and has said he can't do it as the socket is within 150mm of the hob
now looking at the picture , i agree that it looks a little close and looking at it more there is loads of room to the right , however the owner is a little concerned that his freshly tiled back splash will need damaging if it needs to move
any comments welcome , i want to do the correct job , however if the gas man is just being a jobs worth and following recommendations rather than regulations then that would be useful info

image002 2.png
 
View attachment 43683
This one from NHBC.
It’s what we are required to follow on new builds and similar in my area.

Thanks for that .......... don't remember seeing that before ......... shame its not in BS 7671 - as it would clear things up and remove ambiguity...

That said, space permitting I won't put sockets or switches within 300 mm of hobs
 
i wouldnotfit a socket above the sink drainer anyway. it's a splash hazard and encourages customers to use a kettle on the drainer. (NHBC diagram #2).
 
Thanks for that .......... don't remember seeing that before ......... shame its not in BS 7671 - as it would clear things up and remove ambiguity...
I don't suppose that would be in the remit, maybe in an appendix as rough guidance, but even then people would quote it as law.
By putting it as suitable for the location and influences it puts the onus on the designer to think about the possibilities and work appropriately.
Since it's a gas guy complaining, he should justify it and specify a bs7671 reg, gas reg, or information from the instructions of the socket or hob to justify. There should be a technical support line to help if he's needing assistance.
Specifying everything in the regs is a fine balance between taking away flexibility and giving people clear guidance that only needs a ruler to comply.
 

Reply to Hob combustable zone and socket outlet in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock