Hello all, as part of a rewire at the moment, client wants a supply for a hot tub, about 6m from house, aswell as a weatherproof socket outlet (>2m from hot tub). As the hot tub requires a 13A supply I need to provide a separate circuit for it. Only two options I have come up with are to run two separate 2.5mm radials in SWA - one to the hot tub isolator switch and the other to the socket. 16A mcb on each back at the CU.
I was hoping to reduce this to a single supply cable, but I can't think of any way to do this other than to run a single 4mm 32A radial into another consumer unit containing two 16A MCBs which means the hassle of building a weatherproof area to house it. I don't think it's a good to spur the socket off the hot tub supply as fixed equipment over 2000w should have it's own dedicated circuit. Anyone think of a neater solution I may be overlooking?
I was hoping to reduce this to a single supply cable, but I can't think of any way to do this other than to run a single 4mm 32A radial into another consumer unit containing two 16A MCBs which means the hassle of building a weatherproof area to house it. I don't think it's a good to spur the socket off the hot tub supply as fixed equipment over 2000w should have it's own dedicated circuit. Anyone think of a neater solution I may be overlooking?