Customer is wanting a feed to his workshop at the bottom of his garden, he has specified for 6 twin sockets and two 4ft fluorescent lights.

Going to run a SWA from his main CU in the house, then convert to pvc conduit inside the workshop feeding the sockers and feeding the two fluorescents from a FCU.

His main piece of equipment is rated at 1800w and he will be using a handful of power tools in there, obviously not all at once.

The run to the workshop from the house is 20m.

my question being what type of diversity would you use in relation to calculating the Ib

Thanks
 
Diversity isn't an issue as you would only require 1 power circuit, use I(n) protective device rating for your cable calcs. 6mm armouredcable with
design current of 32A will give volt drop of 4.7 volts over 20m which is within 3% limit for lighting. A lot of people fit a board for these type of installs
but a radial power circuit with a fused switch for lighting is perfectly acceptable and cheaper.
 
There should be no issue with stroboscopic effect from the tools he has described to me, but I will be mentioning it if he's planning on having any rotating machinery ect, how would you get round the issue tho with it only being single phase? Yeh the main reason behind the one radial circuit is trying to keep the cost down, using the tabels in the OSG i got:

Ib=39.313 (13a + 5 x 6.5 for the sockets) + (0.313 for two 38w florrys)

In= going for a 40a 60898 mcb

Iz= 49a based on 6mm two core swa, with 7.3 mV/A/m, from appendix 4

so, 39.313 < 40 < 49

volt drop= 7.3 x 39.313a x 20m / 1000 = 5.7v which is within 3% for lighting

Anybody see anything wrong with this?
 
I assume your fitting a local DB, then add up your final circuit protection devices in the sub board and multiply by 0.4 so if you had 32amp sockets and 6 amp for lights it would be 38*0.4 = 15.2 amps. Old rule of thumb and IMO still works.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Ib of radial circuit supplying workshop
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
Scott Fitz,
Last reply from
Engineer54,
Replies
26
Views
6,718

Advert

Back
Top