You've lost me here Midwest, what's 528 got to do with it?.
Discuss Incoming Gas cross bonded off cold water in the Electricians' Talk area at ElectriciansForums.net
You've lost me here Midwest, what's 528 got to do with it?.
Apologies, did misinterpret your post.I completely agree mate. I would bond the internal copper even if it turned into plastic as it exited the building. However, I thought wire puller was getting at the suitability of the main gas bond to carry large fault currents, and presumably because he was stressing TNCS he meant if the neutral (and hence main earth) was lost the pipe route was not reliable, but if it's plastic outside it won't anyway will it?
none required mate. Not sure if this is all worth getting worried about, as others have said. The pipe works all connected at the boiler anyway and any part of it in any installation could easily be disrupted by plumbing activity. How many people have ever seen or heard of a neutral being lost anyway??Apologies, did misinterpret your post.
seems logical to meIn my own house the CU and boiler are in one cupboard, the gas meter in a separate cupboard on opposite side of kitchen and incoming water at other end of the room. On my last Elecsa assessment I asked if i could bond from MET to the gas at boiler and onto water at boiler and confirm continuity to incoming water and gas and the assessor said put note on cert and all would be fine.
I completely agree mate. I would bond the internal copper even if it turned into plastic as it exited the building. However, I thought wire puller was getting at the suitability of the main gas bond to carry large fault currents, and presumably because he was stressing TNCS he meant if the neutral (and hence main earth) was lost the pipe route was not reliable, but if it's plastic outside it won't anyway will it?
I don't have a regs book handy either....but I am certain this applies to supplementary bonding only, not main bonding.
come on then W/P, how under normal conditions can a TNCS system have "significant" current flowing through the EB?Nothing to do with fault currents,on a TNCS system the bonding conductors may carry a significant current under normal load conditions,thats why there is a requirement for 10mm.
come on then W/P, how under normal conditions can a TNCS system have "significant" current flowing through the EB?
come on then W/P, how under normal conditions can a TNCS system have "significant" current flowing through the EB?
A proportion yes, but I don't think the word significant is particularly apt under normal conditions?Because main bonding is connected to a metallic service at or near earth potential, and is electrically connected to the neutral terminal. Therefore a parallel path is created through which a proportion of the neutral current may divert. Do you think the required CSA of TNCS/PME bonding conductors are increased over TT/TNS for fun?
A proportion yes, but I don't think the word significant is particularly apt under normal conditions?
A proportion yes, but I don't think the word significant is particularly apt under normal conditions?
cheers Spin, I wasn't thinking of the bigger picture here. Methinks I might get me a copy of GN7Due to the fact that the network neutral and earth are combined, any neutral current from the installation, will also be present in the earth conductors.
If incoming services are metallic and bonded, then diverted neutral currents from other installations that are bonded to the same services will also be present in the earth conductors.
A break in the Cobined Neutral and Earth network conductor is another kettle of fish.
I know what to do here. Install a bonding clamp on gas pipe with a short piece of 1mm connected to it. Tell kitchen fitter it is an aerial for your wireless bonding arrangement back to MET. He will definately believe you as he does not understand electrical type stuff thingys. Then tell customer it is free. Everyone will love you.