On a new install of a shower circuit, with a neon isolater, is it better to use choc blocks to bypass neon isolater or would it be ok to just test live-earth (live being neutral and live combined) and miss the live-live test?

If testing just live-earth, would you write it down in details of departures that live-live was missed and would you just put n/a in the schedule of tests under live-live test?

Thanks in advance.
 
It would not be a departure to test LN-E as the regulations permit this method. If I use this test it is stated in the extent of work and 'lim' is recorded in the L-N test result in the schedule. However I normally use this method only on existing circuits, on a new circuit where there are no worries over unknown connected equipment I will test L-N and disconnect loads/neons. An exception would be lighting where it's likely control gear/drivers etc will already be connected before IR tests are carried out and would be impractical to disconnect.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
insulation resistance test on shower circuit with neon isolater
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
n180,
Last reply from
ChrisElectrical88,
Replies
5
Views
5,589

Advert

Back
Top