The earthed metal would surely be bonded if extraneous, no?Probably a basic question
In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal
What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
It's either extraneous or it isn't.Probably a basic question
In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal
What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
By earthed metal, I assume you mean metal that is connected to the MET?Probably a basic question
In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal
What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
By earthed metal, I assume you mean metal that is connected to the MET?
For example: plastic incoming supply pipework, metal pipework to boiler, boiler connected to MET via CPC.
The metal pipework is not an extraneous part, so not introducing an extraneous potential. It is however connected to the MET via the boiler and CPC. All that bonding would do is connect it to the MET again, achieving the same thing
If metalwork is directly connected to earthed metal, what would be the point?Probably a basic question
In an installation with pipework or cable ladder that's not extraneous as such but is connected to earthed metal
What's the logic for not main bonding it as the metalwork can surely introduce a potential in a fault situation?
I believe so. Here's how I see it:Will it achieve the same result in the event of a fault?
The CPC connected to boiler or a main vond connected to the metalwork that's not extraneous
I'm just presuming 'earthed metal' to be part of the earthing system. If something needs bonding, it's not.I'll say the same as I did in #3
Without an actual measurement, we don't know if it's extraneous or not.
I don't really know if they meant earthed as in to the Met or Earthed as in Terra Firma, which is why I asked the question.I'm just presuming 'earthed metal' to be part of the earthing system. If something needs bonding, it's not.
Yeah, plenty of folk don't know the difference between earthing and bonding, though.I don't really know if they meant earthed as in to the Met or Earthed as in Terra Firma, which is why I asked the question.
Not extraneousIt's either extraneous or it isn't.
Have you measured it ?
If you have one hand on a live piece of metal and another on a pipe that's earthed via the boiler, then you're going to get one of the worst types of shock you can have, one that's across your chest.So you've got 1 hand on the pipework and another on say a piece of live exposed metal