Steel columns for building into concrete… no inter- connection of Beams … Wooden beams used for interlinked supports … would MBPC be required to each column…
 
Interesting situation, as each of those columns in to a concrete base would defiantly count as an extraneous conductive part. My view is though ought to be bonded as I guess they are all within some sort of distance that contact with the installation's CPC system is possible.

They would not all need to go back to the MET but probably you could zig-zag some bonding from MET to one column and then across wood beam tops or similar to link them all up in some pattern with (hopefully) sane length of bond wire.

Is it TN-C-S ?
And is it needing more than 10mm bond?
 
Interesting situation, as each of those columns in to a concrete base would defiantly count as an extraneous conductive part. My view is though ought to be bonded as I guess they are all within some sort of distance that contact with the installation's CPC system is possible.

They would not all need to go back to the MET but probably you could zig-zag some bonding from MET to one column and then across wood beam tops or similar to link them all up in some pattern with (hopefully) sane length of bond wire.

Is it TN-C-S ?
And is it needing more than 10mm bond?
Yea …. It’s an existing building dating back some years … never got a mention before..came up on EICR… linking these columns approx 300m 10mm Earth cabling… quite a job… will test to see if they are extraneous
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
MBPC to steel columns in warehouse area
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
cliffed,
Last reply from
pc1966,
Replies
3
Views
1,295

Advert

Back
Top