Discuss mortgage retention advice for current installation upgrade in the UK Electrical Forum area at ElectriciansForums.net
If your 'mate' has done you a condition report he should of listed all the defects and codedthem as c1,c2,c3 or further investigation required. Any c1 or c2 would require work to give you a satisfactory certificate, c3 or FI can be left as is and your installation would comply.
with regards to your breakers, why not just swap those cb's for rcbo's and save yourself a fortune, MG still manufacture those and are readily available. Although I'd suggest you get advice on which size breakers you can use, as 6mm t&e clipped direct cannot be placed on a 50a cb/Rcbo let alone 60a
he has been yesterday and will be back on thursday to complete any paperwork he asked me to do the things like put shower on rcd and lights in bathroom and put a 10mm cable in for the shower while i was carrying out any upgrades and then would complete the condition report.
need to check the o.s.g for the correct reference method and then work out volt drop and make sure the In Ib and design current are correct and suitable for the shower installed it is clipped to the wall and goes straight into the loft accross a beam and down into a double pole switch maximum is 7m
do you think i should put both the socket ring finals on rcbos too? and the bathroom lighting c.b. too (or can i leave that as i was planning on fitting selv lighting in there anyway, guys can anyone help me what are the best fans for bathrooms where the shower is obviously causing alot of damp within the bathroom here have a look i was thinking maybe an inline fan but alot of people say they are rubbish
Think you'll find that MG RCBO's are on the expensive side. ..lol!! Those 60A breakers are sitting on 10mm cables if i'm not mistaken!!
im looking the biggest ones i can find are 50A RCBO MG, can you tell me for RCBO do you need seperate nuetral bars like you do on an split twin rcd c.u
Have to put what power rating your shower is, in past posts & ive just missed it?? im having an off day...
guys i have just spoke to my local supplier nbelectrical who have informed me that the highest rcbo that they supply is 45A wylex they dont have any 50A RCBOs so it doesnt look like there would be any other options, as no 1 c.b is 60A supplying a two bedroom house basically i would want that replacement minimum again, considering it has an electric hob with another 6mm cable. the main house electric hob on the cooker 6.0mm has been connected to a fuse spur for the ignition an the gas hob but cable been left in all the way to the d.p switch
From these 2 queries, are you sure you are competent to be doing this? Just a question, not having a go. Daz
* "on rcbos too? and the bathroom lighting c.b. too (can i leave that as i was planning on fitting selv lighting in there anyway?"
* "can you tell me for RCBO do you need seperate nuetral bars like you do on an split twin rcd c.u"
Originally Posted by DPG
What's the second cable going in to that 1st breaker? Daz
it is a feed for the small consumer unit to the right of the main c.u, which is responsible for the ring, that feeds the outside floodlights
so 60A breaker protects 2.5mm2 cable? No good is there, stick in 16A or 20a breaker
well the rcbo has its own n out so i guess the answer is no you dont (but come on we do all have moments and this is my second year doing electrical i am a formulation chemist by qualification
Reply to mortgage retention advice for current installation upgrade in the UK Electrical Forum area at ElectriciansForums.net
Hi All, looking for some assistance on this as finding different information wherever i look. We have a garage external to the house, which we...
4K
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
  • Locked
5K