So why are you trying to fit a 50A or higher MCB/RCBO?
a 45A would be adequate for now but i would in the future like to upgrade the shower to a 10.5kw but if i was going to upgrade the lot now i would put a 10mm cable in and change the pull down d.p to a wall mounted one and also get the correct breaker from the initial installation
 
So why are you trying to fit a 50A or higher MCB/RCBO?
6mm 47A clipped direct and then voltage drop wouldnt have an advers affect over that distance, so a 45A c.b would be acceptable
8500/230=36.96A so 37A maximum current flowing
on 10.5kw/230=45.65A
10mm cable clipped direct 2c0re 63A 3core is 57A
 
Last edited by a moderator:
I dont mean this in a sarcastic way, but what is the fascination with people wanting to get a bigger and bigger showers. What is wrong with a 8.5kw?
 
6mm 47A clipped direct and then voltage drop wouldnt have an advers affect over that distance, so a 45A c.b would be acceptable

Until you want to upgrade your shower to 10.5kw.
 
I dont mean this in a sarcastic way, but what is the fascination with people wanting to get a bigger and bigger showers. What is wrong with a 8.5kw?

Why anyone would ever need a 10.5KW shower, i will never know!! I'm using a 4.2KW shower over here and it's more than just adequate for a good hot shower!!
 
Why anyone would ever need a 10.5KW shower, i will never know!! I'm using a 4.2KW shower over here and it's more than just adequate for a good hot shower!!

Maybe they want to re-enact a scene from Rambo, when he is in the police station...
 
Bet they don't sell many 10.5KW showers in France, where it seems the average domestic supply is limited to 12KVA!! ...lol!! ....It's only the daft British that want to be one better than the Jones next door!!! lol!!
 
OP: Id be more concerned about the 2.5mm cable going to MCB 1 (60A) for the outside lights than the shower cable.
 

Reply to mortgage retention advice for current installation upgrade in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, looking for some assistance on this as finding different information wherever i look. We have a garage external to the house, which we...
Replies
22
Views
4K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
521
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
271
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Replies
4
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock