OP
Engineer54
So why are you trying to fit a 50A or higher MCB/RCBO?
Yep, a 40A MCB will be more than adequate for that size of shower!!
Discuss mortgage retention advice for current installation upgrade in the UK Electrical Forum area at ElectriciansForums.net
So why are you trying to fit a 50A or higher MCB/RCBO?
a 45A would be adequate for now but i would in the future like to upgrade the shower to a 10.5kw but if i was going to upgrade the lot now i would put a 10mm cable in and change the pull down d.p to a wall mounted one and also get the correct breaker from the initial installationSo why are you trying to fit a 50A or higher MCB/RCBO?
6mm 47A clipped direct and then voltage drop wouldnt have an advers affect over that distance, so a 45A c.b would be acceptableSo why are you trying to fit a 50A or higher MCB/RCBO?
6mm 47A clipped direct and then voltage drop wouldnt have an advers affect over that distance, so a 45A c.b would be acceptable
I dont mean this in a sarcastic way, but what is the fascination with people wanting to get a bigger and bigger showers. What is wrong with a 8.5kw?
Why anyone would ever need a 10.5KW shower, i will never know!! I'm using a 4.2KW shower over here and it's more than just adequate for a good hot shower!!
OP: Id be more concerned about the 2.5mm cable going to MCB 1 (60A) for the outside lights than the shower cable.