I have an an electric brake on a three phase motor with the attached wiring schematic which is part of a wine press. At first I thought this was the Wye/Delta wiring layout but I am starting to think this is actualy a low/high voltage schematic but they are using the wye/delta symbols. There is no neutral shown on the schematic for the brake nor is there one in the press itself. I am a bit confused at this point.Brake Tag.jpgBrake Wiring.jpg
 
It is both,
star configuration for 400v (3 phase)
delta for 230v (3 phase)
the brake is not mentioned in your pictures, often the brake is fed from a rectifier off the windings so the brake coil is energised and the brake turned off when the motor is powered and is spring activated when power is released.
 
It is both,
star configuration for 400v (3 phase)
delta for 230v (3 phase)
the brake is not mentioned in your pictures, often the brake is fed from a rectifier off the windings so the brake coil is energised and the brake turned off when the motor is powered and is spring activated when power is released.
I have 208V Three Phase. The brake is wired directly to the terminals inside the motor wiring box. Thanks for the info on the star for higher voltage and delta for lower voltage. That is the answer I was looking for.
 
208v might be a little low for that motor, if it is loaded anywhere near its maximum rating, i would expect it to overheat.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Lake Chelan WA
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
If other, please explain
I am a HydroElectric Power Plant Operator and I have wired my own 8400 sqft commercial building....so a bit more than a DIY Homeowner but not a professional electrician