Discuss My electrician wants to remove the inverter's supply PE and... in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
1
...Replace it with a connection to a ground spike via the heat sink.

The 1.5kW GTI has no off grid capability.

This separates the house PE from the inverters but is it the right thing to do?

New to the forum, this is my first post.
 
This sounds dodgy to me.

Do you have any more details? Why do they want to do this?
Its complicated...The DNO supply is TN-C-S, recently a ground spike was connected to the GTI and it operated without problem. During renovation and unknowingly the PE to the incoming copper water pipe was cut. This manifested itself as nuisance tripping of the consumer unit RCD. When the spike was disconnected the nuisance tripping went away. The sparks is due to reconnect the water pipe PE next week. It seems the only way the TN earth could connect to ground was through the GTI supply cable and its earth wire. I agree disconnecting the GTI earth is suspect it will remain connected; the ground spike will remain disconnected. I'm hoping to have it repurposed as a supplemental PE to the DNO earth in the meter box.
 
Have any checks been done on the incoming supply and also the inverter output, it seems odd that your installation is relying on a metal water pipe for an earth and would possibly suggest a floating neutral and it is the water pipe that is giving it an earth reference
I would suggest it is a back to basics approach and check the incoming supply and maybe a check at 1 or 2 neighbours if you can, I suspect there is a DNO fault outside your property on the local network
With regard to making your earth rod a supplemental earth to the MET while the idea has some merit it could mask any future faults on the local supply network and your rod could become the main earth point for a number of adjacent properties and potentially end up carrying quite a high fault current. I have seen the same set up a few years back where an electrician couldn't be bothered calling the DNO about an earth fault and instead installed a rod and connected it to the MET the result was 6 -8 houses were earthed via that rod with a Ze of 37Ω
 

Reply to My electrician wants to remove the inverter's supply PE and... in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
916
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
398
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock