...Replace it with a connection to a ground spike via the heat sink.

The 1.5kW GTI has no off grid capability.

This separates the house PE from the inverters but is it the right thing to do?

New to the forum, this is my first post.
 
This sounds dodgy to me.

Do you have any more details? Why do they want to do this?
Its complicated...The DNO supply is TN-C-S, recently a ground spike was connected to the GTI and it operated without problem. During renovation and unknowingly the PE to the incoming copper water pipe was cut. This manifested itself as nuisance tripping of the consumer unit RCD. When the spike was disconnected the nuisance tripping went away. The sparks is due to reconnect the water pipe PE next week. It seems the only way the TN earth could connect to ground was through the GTI supply cable and its earth wire. I agree disconnecting the GTI earth is suspect it will remain connected; the ground spike will remain disconnected. I'm hoping to have it repurposed as a supplemental PE to the DNO earth in the meter box.
 
Have any checks been done on the incoming supply and also the inverter output, it seems odd that your installation is relying on a metal water pipe for an earth and would possibly suggest a floating neutral and it is the water pipe that is giving it an earth reference
I would suggest it is a back to basics approach and check the incoming supply and maybe a check at 1 or 2 neighbours if you can, I suspect there is a DNO fault outside your property on the local network
With regard to making your earth rod a supplemental earth to the MET while the idea has some merit it could mask any future faults on the local supply network and your rod could become the main earth point for a number of adjacent properties and potentially end up carrying quite a high fault current. I have seen the same set up a few years back where an electrician couldn't be bothered calling the DNO about an earth fault and instead installed a rod and connected it to the MET the result was 6 -8 houses were earthed via that rod with a Ze of 37Ω
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
All Other Countries (This Is English Speaking Website Only - WE don't mind Google Translate Users :)
What type of forum member are you?
Other

Thread Information

Title
My electrician wants to remove the inverter's supply PE and...
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Joules,
Last reply from
UNG,
Replies
3
Views
1,386

Advert

Back
Top