Hi folks, adding new lighting circuit to distribution board in small rented commercial property. There's a dist board in this property however main board and point of origin are in an adjacent rented out small commercial building that is difficult to access. Landlord has keys etc but as it's leased to a tenant who is not often there, is reluctant to let me in, even though he's supposed to etc. Can I sign off when not able to access the main board and point of origin or is it a showstopper? If I can proceed without access to main board, how to consider this limitation on the Minor Works Certificate? Many thanks! SW
 
Hi folks, adding new lighting circuit to distribution board in small rented commercial property. There's a dist board in this property however main board and point of origin are in an adjacent rented out small commercial building that is difficult to access. Landlord has keys etc but as it's leased to a tenant who is not often there, is reluctant to let me in, even though he's supposed to etc. Can I sign off when not able to access the main board and point of origin or is it a showstopper? If I can proceed without access to main board, how to consider this limitation on the Minor Works Certificate? Many thanks! SW

Well for a start, you can't use a MEIWC if you are installing a new circuit. It will need to be an EIC I'm afraid.
 
Yep, ok, bashing out a post before rushing off to a job and got it wrong. Any helpful input?
 
the main info you can't get is Ze, and the main OCP fuse details. best you can do is enter N/V for the main fuse, and enter a figure for Zdb and PFC at your accessible board.
 
Yep, ok, bashing out a post before rushing off to a job and got it wrong. Any helpful input?

Well, I'm sorry that you did not find my post helpful. I was not trying to be picky, it was just that having recently read the Chief Examiners report from the last 2391 exam, this was something that they picked up on, and it has therefore stuck in my head.

The EIC has different reporting requirements, as I'm sure you are aware, regarding supply characteristics.
'Nature and type of live conductors' being one that is impossible to ascertain without access to the main intake. So in other words, using the correct document is putting additional demands on your work, and your problem, that an MEIWC wouldn't. That is why I mentioned it.

Cheers
 
Last edited by a moderator:
Hi, apologies for my morning curtness. As it happens I'm using a NAPIT mweic/prov of single circuit certificate so it's a moot point. I'll record per tele's advice. Cheers.
 
Hi, apologies for my morning curtness. As it happens I'm using a NAPIT mweic/prov of single circuit certificate so it's a moot point. I'll record per tele's advice. Cheers.

No problem, and no apology necessary. From your point of view, given what you've said about NAPITs form, I can see how my post wouldn't have been seen as giving the advice you needed. Anyway, I hope it all goes smoothly.

Cheers
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New Circuit of Distribution Board But Can't Access Main Board
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
SW1970,
Last reply from
mogga,
Replies
7
Views
3,547

Advert

Back
Top