If there is no earth class 2 must be used and preferably have the small white caps over the screws, otherwise to use class 1 you'd be looking at getting an earth into the circuit. Of course making sure it is RCD protected also
house or bungalow?
Approx 15 years ago I had the same problem in a bungalow..
All was ok apart from no RCD and no lighting cpc..
I installed an RCD and a separate 1mm cpc for the lighting circuit..
Yes, the homeowner had blown their budget on fancy light fittings and accessories and didn’t realize they all needed to be earthed..1mm cpc?
The metal back boxes may have nylon type lugs for the front plate screws, if thats the case then they do actually do metal over plates that you mount on the front.... Not the prettiest but if you dont like your white switches and dont want a rewire its an option
Definitely go for an inspection, you will then be given a report with all observations, recommendations, etc
I installed an RCD and a separate 1mm cpc for the lighting circuit..
Don't the regs say something about if you have to run a separate earth it had to be 4mm.. or something like that??
4mm if run outside of containment I believe ?