Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and have a relatively good understanding of the regulations, that said I have been working for myself until recently and now work for a company that completes disability adaptions including bathrooms, stairlifts, hoists etc. Previously when I encountered old rewireable fuse boards and the clients requirements were additional circuits or alterations to special locations I would either upgrade the existing system or turn the work away. My reasoning for this is adding separate consumer units for a kitchen, bathroom, outside lighting etc is nothing more than a "work around" to the installation and increased risk of customers or future electricians interconnecting between, complicated isolation of circuits/ areas within the property, any existing faults not rectified and so on. This is a personal preference only and I understand that not all would agree with me and some may even claim I am scare mongering clients into unnecessary work and cost, but this is not the case.

I have encountered some existing rewireable fuse boards that in reality are in desperate need of updating and possibly a partial or full rewire in my opinion. I have attached 2 images that I hope will help.

• Example 1 -- TT arrangement, no main earth, no bonding on water (well, there is a 4mm cpc connected in board to a pipe upstairs under the boiler, but not what id consider suitable at all), no bonding to gas, charring/ blackening of cables, no 100ma rcd, sockets on lighting circuit with no cpc (old rubber singles) amongst other issues.

I am tasked with installing a switched fused spur for stairlift only

• Example 2 -- TT arrangement, incoming tails are different csa, enter the board at 3 separate places, no 100ma rcd, warning label from British Gas, upon arrival I noticed 3 x 2.5mm radial circuits supplied by 30A cartridges (I exchanged these to 15A and 20A), external lights that have the glass bezels open and damaged etc.

I am tasked with installing new 9.5kw electric shower, bathroom light, extractor fan

I have to arrange for the DNO to remove the main fuse at both properties including installation of new 100A main isolator. My question is, to my understanding a new CU woth spd and 30ma rcds do not require a 100ma rcd provided the incoming tails are secured to minimise them becoming loose, an 100ma time delay rcd would be needed if installed in front of the sub board (though a new CU with 30ma does not require this). If I install new main earthing to existing board it may create a "circuit" to earth if there are faults to the existing installation, any rcd installed in front of the existing installation will likely trip due to existing faults, should the existing tails (different csa) be replaced.

To what extent am I responsible for responsible to the existing installation?

Personally I wouldn't feel comfortable re connection of installations that I know have these issues, even though technically as I'm only working on the new sub boards and no alterations are made to the existing installation.

Any help or advice would be appreciated, thanks in advance
 

Attachments

  • 20230511_141112.jpg
    20230511_141112.jpg
    247 KB · Views: 331
  • Screenshot_20230511_145557.jpg
    Screenshot_20230511_145557.jpg
    404.8 KB · Views: 120
  • 20230511_124154.jpg
    20230511_124154.jpg
    253.6 KB · Views: 109
  • 20230511_124132.jpg
    20230511_124132.jpg
    259.9 KB · Views: 159
  • 20230511_124138.jpg
    20230511_124138.jpg
    237.3 KB · Views: 115
  • 20230511_130907.jpg
    20230511_130907.jpg
    224.5 KB · Views: 120
  • 20230511_131113.jpg
    20230511_131113.jpg
    172.3 KB · Views: 136
  • 20230511_131546.jpg
    20230511_131546.jpg
    248.1 KB · Views: 124
  • 20230511_131504.jpg
    20230511_131504.jpg
    200.9 KB · Views: 127
  • 20230530_165741.jpg
    20230530_165741.jpg
    293.3 KB · Views: 174
  • 20230530_165458.jpg
    20230530_165458.jpg
    321 KB · Views: 126
  • 20230530_165449.jpg
    20230530_165449.jpg
    315 KB · Views: 126
  • 20230530_165447.jpg
    20230530_165447.jpg
    295.5 KB · Views: 178
  • 20230530_151958.jpg
    20230530_151958.jpg
    376.7 KB · Views: 181
  • 20230530_151951.jpg
    20230530_151951.jpg
    347.1 KB · Views: 124
The original point of my post is that the DNO don't seem to be supplying an adequate/maintainable earth to any dwelling, old or new, it just seems a recurring theme on this Forum.
 
is it time for legislation for new builds to all have a TT supply, discuss?
In general, new builds are PME from the get-go, so it's not totally fair to say the DNO don't care about providing an earth. The argument is usually over old service heads where for them to take responsibility could be economically costly.

AM2 does add a recommendation to add a backup earth rod to TN systems. New builds actually would be ideal candidates for following this. At the moment NAPIT are advising members not to try and add rods to existing TN properties for fear of hitting services.

I don't think I'll ever regard TT as anything other than 2nd choice. I don't particularly trust RCDs that have sat their for years, wouldn't like to be relying on them for fault protection in ideal circumstances.
 
In Rural France I would say that nearly all the installations are TT with an up front S type RCD, the supply is such that if you try to draw more than your allowed A the RCD will trip out, so it gets tested every-time you put on all your white goods at once, seems washing day is always associated with putting on the dishwasher as well. 🤔
 
Hitting services is the main thing spoken about.
I also know it was a controversial addition and some on the committee were opposed to it. I didn't get to hear exactly why.
There is always someone opposed to any change, what would be nice (but unlikely to happen) would be the BSI committees providing a written rational for the decisions for or against any given proposal.

I can see a real risk from proposing adding rods to existing properties due to service pipes and cables, etc, but where they really dropped the ball was not mandating a decent earth to be incorporated in any new builds. I think for years the USA has required bonded rebar in concrete foundations and aspects like that would not have been difficult to do at the build stage, could have provided fairly good Ra values, and over time made a big difference to the safety of PME systems.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
APT Building and Electrical

Thread Information

Title
Old rewireable fuse boards, alterations and additions
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
Rhino-Spark,
Last reply from
ipf,
Replies
28
Views
6,957

Advert

Back
Top