New 32a C RCBO 4mm T&E radial laundry circuit, in order to take the load off a ring I installed the aforementioned, 5 doubles for dryers, washers and a roller press, 3 washers 2 dryers in total and well under 32a I install a C to deal with any motor start/ stop reverse etc and heaters, top reading is .77 on the end not over by much but it still annoys the hell out of me .58 at the first, end socket is a little roller press a shade over 1500w , So would you drop to a B or leave it as is ?
Pict
 
New 32a C RCBO 4mm T&E radial laundry circuit, in order to take the load off a ring I installed the aforementioned, 5 doubles for dryers, washers and a roller press, 3 washers 2 dryers in total and well under 32a I install a C to deal with any motor start/ stop reverse etc and heaters, top reading is .77 on the end not over by much but it still annoys the hell out of me .58 at the first, end socket is a little roller press a shade over 1500w , So would you drop to a B or leave it as is ?
Pict

Its covered by a 30mA RCBO 50V/30mA=1667 Ohms. Its not ideal from a design point of view as its a new circuit on TN system but hey I wouldn't be loosing any sleep over it. Its covered by the RCD max Zs value.....
 
  • Like
Reactions: 1 person
try the alternative hi-current test. short l-e at last socket ( with RCD and MCB OFF ), then measure across RCD Lin and MCB Lout.

High current Zs test with RCD.jpg
 
Last edited:
try the alternative hi-current test. short l-e at last socket ( with RCD and MCB OFF ), then measure across RCD Lin and MCB Lout.

View attachment 32727

You love that diagram Tel!;)

I think Richard better put a patent on it pretty darn quick:)
 
  • Like
Reactions: 2 people
Is that 4.0 T&E surface fixed cos if it ain't it doesn't want to be on a 32A device no matter what religion it is.
 
Is that 4.0 T&E surface fixed cos if it ain't it doesn't want to be on a 32A device no matter what religion it is.
buried in a non-insulating wall.e.g. plaster, still counts as ref.method C.
 
Throughout it's run, from the consumer unit and any cavities?
 
New 32a C RCBO 4mm T&E radial laundry circuit, in order to take the load off a ring I installed the aforementioned, 5 doubles for dryers, washers and a roller press, 3 washers 2 dryers in total and well under 32a I install a C to deal with any motor start/ stop reverse etc and heaters, top reading is .77 on the end not over by much but it still annoys the hell out of me .58 at the first, end socket is a little roller press a shade over 1500w , So would you drop to a B or leave it as is ?
Pict

Is a C type sufficient to cope with motor inrush? I think it rarely is in practice, but presumably you have actually calculated this rather than guessing?

What did your design calculations come up with for this circuit? Presumably they indicated that it should meet the required Zs which then suggests there is a problem with the circuit.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

the pict

Mentor
~
Joined
Location
Brodick
Business Name
Devlin Maguire Electrical

Thread Information

Title
one of those sodden zs teeth grinding days
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
10

Thread Tags

Tags Tags
those

Advert

Thread statistics

Created
the pict,
Last reply from
davesparks,
Replies
10
Views
1,755

Advert