Opinions please.

Discuss Opinions please. in the UK Electrical Forum area at ElectriciansForums.net

Dave OCD

-
Mentor
Esteemed
Arms
Reaction score
6,671
I have an extension to wire this week which is a garage conversion comprising a study, shower room and small store area. The supply is TT and I'm intending on running a 16mm sub main from the existing mains position under the suspended floor through the hall in the house and installing a new small CU with RCBOs in the new store area. Due to the earthing arrangements I'll fit an S type 100ma RCD and 60a Switch-fuse [possibly 63a MCB] at the supply end, either seperate units linked by tails or integrated in one unit if I can source something suitable. Do you think these items should be Amendment 3 compliant as I don't think I've seen such a beast yet ? Any pointers to similar recently used kit would be welcome. :smilewinkgrin:
 
I used one of these recently on a job. Tails in the top using Wago sprint glands in one knockout. 16mm SWA glanded at the bottom. Comes with 3 fuses and mine had a metal hinged door on it rather than the plastic in the picture.

https://www.tlc-direct.co.uk/Products/CGFS100.html



Only downside is it is a bit big if your tight for space.

That could be ideal, could even put the S type RCD in that instead of the 100a DP switch , tin hat on now. :grin:
 
my understanding of the new regulation is that only domestic consumer units and "similar switchgear containing OPD's" need to be of a non combustable construction.

a standalone rcd has a completely different British standard / product definition to a c.u. therefore would fall outside the requirement and a pvc enclosure could be continued to be used.

to put it another way , you may find that on a TT arrangement the dno may prefer or even insist on double insulated upfront isolating / rcd enclosures for obvious safety reasons.
 
Last edited by a moderator:
my understanding of the new regulation is that only domestic consumer units and "similar switchgear containing OPD's" need to be of a non combustable construction.

a standalone rcd has a completely different British standard / product definition to a c.u. therefore would fall outside the requirement and a pvc enclosure could be continued to be used.

to put it another way , you may find that on a TT arrangement the dno may prefer or even insist on double insulated upfront isolating / rcd enclosures for obvious safety reasons.

Where did you get the 'containing opds' bit from? It doesn't say that in the regs.

A standalone RCD in a 2way enclosure is very similar switchgear to a CU.

Why would the DNO give a monkeys? After their terminals they really don't worry too much unless your tails are too long or you damage their network somehow
 
Where did you get the 'containing opds' bit from? It doesn't say that in the regs.

A standalone RCD in a 2way enclosure is very similar switchgear to a CU.

Why would the DNO give a monkeys? After their terminals they really don't worry too much unless your tails are too long or you damage their network somehow

The RCD will be going in the same Amd 3 Compliant enclosure as the cartridge fuse, the RCD will take the place of the usual DP switch [100a rated 100ma time delayed] so I'm covered and it'll be a nice tidy solution. :smile:
 

Reply to Opinions please. in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock