For the rcd enclosure you might have to use a two way board and a couple of blanks. Cant seem to find anything compliant.
 
That's what I mean, I've been quoted similar...most wholesalers seem to be trying to rip the arse out if it. These ones are just as good, do exactly the same job and for under £2...cant complain at that.

I actually tried a standard 32mm Wiska plastic gland asan experiment with 16mm tails/10mm earth and found the insert squashes/compresses enough to seal it all up pretty well. [It would certainly meet IP4X]
 
For the rcd enclosure you might have to use a two way board and a couple of blanks. Cant seem to find anything compliant.

That's what I'm thinking Lee, tempting to use a small compliant board with the S type as the main switch and a 63a MCB for the sub main, but compared to a fuse it could cause discrimination issues I think. :smile5:
 
That's what I'm thinking Lee, tempting to use a small compliant board with the S type as the main switch and a 63a MCB for the sub main, but compared to a fuse it could cause discrimination issues I think. :smile5:



That's the problem as even a 6A mcb will offer none to very little discrimination with the 63A mcb...in an ideal world you would put the distribution circuit on a fuse.
 
Is it an actually requirement that the door is hinged to shut itself? Just think if you had to install a 3phase board within a domestic property if this was the case.

No,it's not a specific requirement....but for me that is not complying with the intention of the regulation which is a fire resistant enclosure over all 'combustible' components as far as is practical. That is why all Am 3 designed enclosures I've seen have a top hinged metal lid. I wouldn't fit that wylex unit. I take your point about the 3 phase board,but that would easily be overcome by fitting 3 separate single phase DB's if you took the view that a side hinged door was not compliant. I would take that view as the door left open would negate any fire resistance of exposed 'combustible' components.
 
Last edited by a moderator:
The hinged lid is a good idea but I've already seen a board installed where the wall was out and the lid ever so slightly stayed open. Imo a catch or similar is better. Edit: What switch fuse would you install? As there doesn't appear to be many on the market atm that meet the requirements.
 
Last edited by a moderator: