Been a while since I done a PAT test on a 20meter extension cable and kinda forgot how to do it. The calculation I mean.
 
Welcome to the forum:handwaving:

Assuming you are talking about earth resistance, just look up resistances of lengths of cable in the COP and multiply e.g 1.5mm² is 13.3mohms/m so a 20m length would be 13.3*20/1000 = 0.266 ohms
therefore earth resistance should be 0.366 ohms or less.
 
Welcome to the forum:handwaving:

Assuming you are talking about earth resistance, just look up resistances of lengths of cable in the COP and multiply e.g 1.5mm² is 13.3mohms/m so a 20m length would be 13.3*20/1000 = 0.266 ohms
therefore earth resistance should be 0.366 ohms or less.
 